As above, taking a Zs measurement on a circuit covered by a 10mA rcd. Tripping the rcd on a no trip, three lead test using a Megger 1721. Is there a change in the settings I’ve forgotten about to allow a Zs to be taken. Oh, testing at a socket rather than source.
TIA
 
For some reason I thought there was an option to reduce the test current on the Megger, but it appears there isn’t.
So Ze +(R1+R2) it is.
Thanks guys.
PS can’t remember the last time I had to test with a 10mA rcd in place!
 
If your going to the trouble of linking the line and cpc at the end of the circuit then you may as well measure the R1+R2 and add it to the Ze/zs/zdb or am I missing something ?
If you have the line and cpc linked for R1+R2 then for the sake of a few extra seconds just test the Zs at the device instead of calculating.
 
Is that an approved test method?
Never seen that method before, not in gn3 anyway.
Not sure about GN3 but it is in the book "Practical Guide to Inspection, Testing and Certification of Electrical Installations" It was common practice before the introduction of no trip settings on meters.
 
For some reason I thought there was an option to reduce the test current on the Megger, but it appears there isn’t.
So Ze +(R1+R2) it is.
Thanks guys.
PS can’t remember the last time I had to test with a 10mA rcd in place!

I know you can change the mA, see 5:40 onwards. 10mA is the minimum setting.




Edit: I've just looked through the megger manual & there's no mention of changing the trip current
 
Last edited:
I tend to favour the link out and test at high current method, just because it's what I've done for years, and it gives me a more accurate measurement than the low current test most of the time, also it amazes me sometimes how much an rcd will influence the result if testing both way. BG rcds seem to be the worst for raising the Zs readings!
 

Reply to 10mA rcd tripping on Zs test in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
670
  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
738

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top