If you have the line and cpc linked for R1+R2 then for the sake of a few extra seconds just test the Zs at the device instead of calculating.If your going to the trouble of linking the line and cpc at the end of the circuit then you may as well measure the R1+R2 and add it to the Ze/zs/zdb or am I missing something ?
Is that an approved test method?If you have the line and cpc linked for R1+R2 then for the sake of a few extra seconds just test the Zs at the device instead of calculating.
Not sure about GN3 but it is in the book "Practical Guide to Inspection, Testing and Certification of Electrical Installations" It was common practice before the introduction of no trip settings on meters.Is that an approved test method?
Never seen that method before, not in gn3 anyway.
For some reason I thought there was an option to reduce the test current on the Megger, but it appears there isn’t.
So Ze +(R1+R2) it is.
Thanks guys.
PS can’t remember the last time I had to test with a 10mA rcd in place!