With installations up to and including 100A, there are very few instances where an earthing conductor with a CSA greater than 10mm² would be required.
Those instances are limited to 100A supplies, with a Ze such that disconnection times would be around the 5 second mark, and would often involve the use of multi core cables.
Even in those instances where a CSA greater than 10mm² is required for the earthing conductor, often 6mm² bonding conductors would be acceptable
As Jay Sparks says, conduct the adiabatic equation to determine what CSA is required for the earthing conductor, then size the bonding conductor accordingly.
 
Bgb book states minimum size conductor of 10mm in relation to neutral conductor upto 35mm on a tnc-s system. so basically if its a 6mm main earthing conductor the bonding conductor still has to be 10mm, now tn-s is different no less than half rhe size of earthing conductor , so my question to you is would it be acceptable as long as no thermal damage on a tnc-s system.
 
Bgb book states minimum size conductor of 10mm in relation to neutral conductor upto 35mm on a tnc-s system. so basically if its a 6mm main earthing conductor the bonding conductor still has to be 10mm, now tn-s is different no less than half rhe size of earthing conductor , so my question to you is would it be acceptable as long as no thermal damage on a tnc-s system.
No, with TN-C-S the minimum CSA of 10mm² applies to both the earthing and bonding conductors.
It is only with TT and TN-S, where the earthing conductor can have a smaller CSA than the bonding conductors.

Yes 6mm² would be considered as acceptable if as you say, there are no indications that the conductors have been overheating.
 
I'm trying to understand this particular issue. Surley the earthing conductor and main protective conductors are relative to the supply tails, not the size of the cut out fuse (which the DNO could change)?
 

Reply to 10mm bonding to water and gas in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
625
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
955

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top