Adibiatic equation is not used for main bonding conductors
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss 10mm bonding to water and gas in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
No, with TN-C-S the minimum CSA of 10mm² applies to both the earthing and bonding conductors.Bgb book states minimum size conductor of 10mm in relation to neutral conductor upto 35mm on a tnc-s system. so basically if its a 6mm main earthing conductor the bonding conductor still has to be 10mm, now tn-s is different no less than half rhe size of earthing conductor , so my question to you is would it be acceptable as long as no thermal damage on a tnc-s system.