With installations up to and including 100A, there are very few instances where an earthing conductor with a CSA greater than 10mm² would be required.
Those instances are limited to 100A supplies, with a Ze such that disconnection times would be around the 5 second mark, and would often involve the use of multi core cables.
Even in those instances where a CSA greater than 10mm² is required for the earthing conductor, often 6mm² bonding conductors would be acceptable
As Jay Sparks says, conduct the adiabatic equation to determine what CSA is required for the earthing conductor, then size the bonding conductor accordingly.