10mm bonding | on ElectriciansForums

Discuss 10mm bonding in the UK Electrical Forum area at ElectriciansForums.net

S

sedgy34

may have covered this already but,,,
was wiring a new house today one of the lads pipes up could run the 10mm earth bond from the main earth terminal in the external box to the gas pipe as its 200mm away in the gas box! i said did i just hear right? his response was whats the difference?

so guys your thoughts on his question.
 
Cant see the issue personally.

The installation MET is within the external cabinet whilst the earthing bar in the CU becomes a BEMT. As long as sizes are sufficient and all labelled correctly it's fine.
 
If you transpose this to an industrial situation, ie a water treatment works, then using EMT's is the way to go. The price difference would be substantial. Some of the works I am involved with are very large, and you simply run main bonding from the nearest DB that has a sufficiently sized CPC. Sometimes purpose built earth bars are used. With main bonding ect, the regs make no differientation between domestic & industrial ect. The problem comes when a spark follows your work and because it doesn't comply with the "common practice", then your work will be slated. Regarding this issue though, run it from the external box.
 

Reply to 10mm bonding in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
521
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
680
loz2754
L
  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
2
Replies
23
Views
2K