10mm meter tails 60amp fuse 6mm bond | Page 2 | on ElectriciansForums
Discuss 10mm meter tails 60amp fuse 6mm bond in the UK Electrical Forum area at ElectriciansForums.net
LONDON (barnet)
Afternoon all been a while since I've posted.
at today's job I noticed 10mm meter tails with 6mm bonding and although my first thoughts were tails should be min 16mm and bonding 10mm
so at the risk of sounding stupid I couldn't find the exact reason why this was wrong as the 10mm would take 61amps
could anyone clear this for me?
What matters is whether the cable complies with the requirements.
As cables with insulation and sheaths, and cables with reinforced insulation satisfy the requirements for double insulation, such cables are deemed as being double insulated.
Well if you want to be pedantic then technically speaking an insulated and sheathed cable may be considered to afford equivalent protection to DI subject to some stipulations (which I can't remember) rather than actually being deemed to be double insulated.
Plus reinforced insulation is a separate thing to DI, although the regulations consider them to be equivalent.
V/Ze= 766A
I=766
T=0.16
K=143 (not incorporated in a cable or bunched)
766x766=586756
586756x0.16=93880
square root of 93880=306
306/143=2.13mm for your main earthing conductor.
Taking reg 544.1.1 in to account the 6mm bonding conductor is adequate.
Edit: Based on a BS1361 fuse