10mm T&E CU change. | Page 2 | on ElectriciansForums
Discuss 10mm T&E CU change. in the UK Electrical Forum area at ElectriciansForums.net
Hi,
I've been asked to change a CU in a converted one-bed flat immediately above the cellar which contains the TNS supply. The existing CU is currently supplied by a 6m run of clipped direct 10mm T&E protected by a 63A switch-fuse in the cellar. It's a small flat, haven't worked out maximum demand yet but am guessing about 45A. Main bonding goes direct to a MET in the cellar so I don't think that's an issue.
Just want to check a couple of things:
i) Is there any need for me to upgrade the supply to the CU? Also, do I need to add RCD protection before the new CU even though it's clipped direct?
ii) Is the 4mm cpc in the T&E good enough as the earthing for the new CU?
Thanks.
As this is a separated self contained flat, any main bonding to extraneous pipework within the flat, should be going to that flats EMT, not to the MET of the building. The 10mm T&E's 4mm CPC is therefore in my opinion not suitable. A separate 10mm earth conductor should be provided from the flats CU or EMT to the installations MET... Personally i would never use T&E for supplying self contained CU's in a multi dwelling building...
Reply to 10mm T&E CU change. in the UK Electrical Forum area at ElectriciansForums.net
This charger doesn't support rear entry from the looks, only bottom entry, hence that. Unless they make a white sheathed SWA, I would still need...
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Recommended Sponsor News
Hi everyone,