I know there’s the adiabatic equation to work earth size but generally if you install a twin and earth cable for distribution, do you need to worry about the smaller cpc size
My situation is 20 metre 10mm t and e run and not using it to provide earth bonding. Will the 4mm cpc be adequate. 50A mcb not many circuits to feed.
What's the Ze at source of circuit?
Type/rating of OCPD etc?
Installation method?
Yes you do need to worry about it, whether it be a final or distribution circuit.
Reply to 10mm t&e submain cpc in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...