What size swa would be needed for a 4/5 bed new build property submain burried direct in ground?
 
Sorry for the vague info, i will explain more.The supply is for a 4 or maybe a 5 bed house (100A). Allowing for a 5% vd the cable size would be 50mm.

0.94x110x100/1000 = 10.34

Am i close
 
close, but VD for lighting is 3%, so i'd err on the side of caution. better to install a slightly oversized cable than have to dig out and replace an undersised one.

i got 70mm based on 80A demand.

5.6V drop.
 
I just got an email from the guy. This is the only info i have. I know nothing about whats on site whatsoever so can't comment further .It reads as follows;


I need to put in 5 supplies. One each for the 3 units - these will all be say 3 bed, and no electric heating or showers. They each have a cable run of 75 metres.
One run needs to go to the house - this will be about 110metres, and it will be a 4/5bed house.
The other one needs to go to the sewage treatment plant, which is again about 120 metres, but only needs to run a 200 Watt pump.
Everything single phase.

Why would this be preferable to getting the board in to give new supplies?
 
I just got an email from the guy. This is the only info i have. I know nothing about whats on site whatsoever so can't comment further .It reads as follows;


I need to put in 5 supplies. One each for the 3 units - these will all be say 3 bed, and no electric heating or showers. They each have a cable run of 75 metres.
One run needs to go to the house - this will be about 110metres, and it will be a 4/5bed house.
The other one needs to go to the sewage treatment plant, which is again about 120 metres, but only needs to run a 200 Watt pump.
Everything single phase.

Why would this be preferable to getting the board in to give new supplies?

you need a site meeting mate and deisgn it correctly, also submains are cheaper than paying the dno
 
we all get a brain fart now and then. best to be sure before doing than make a cock -up

- - - Updated - - -

This will help you out in times of rustyness.

Cable-Mate

or AEI cable finder on line, it's free.
 

Reply to 110 metre submain for 4/5 bed new build? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
841

Similar threads

  • Question
If it is TT then you can use the armour of any of them as CPC but will almost certainly need an up-front delay RCD at the sub-main feed point to...
Replies
5
Views
940
  • Question
Good luck with your project and I’m starting in 2 weeks to install the same thing as you.
Replies
3
Views
858

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top