Just researched this breifly. the following paragraph sums it up.

Operation of the motors above rated name plate speed (base speed) is possible, but is limited to conditions that do not require more power than nameplate rating of the motor. This is sometimes called "field weakening" and, for AC motors, means operating at less than rated volts/hertz and above rated name plate speed. Permanent magnet synchronous motors have quite limited field weakening speed range due to the constant magnet flux linkage. Wound rotor synchronous motors and induction motors have much wider speed range. For example, a 100 hp, 460 V, 60 Hz, 1775 RPM (4 pole) induction motor supplied with 460 V, 75 Hz (6.134 V/Hz), would be limited to 60/75 = 80% torque at 125% speed (2218.75 RPM) = 100% power.[13] At higher speeds the induction motor torque has to be limited further due to the lowering of the breakaway torque of the motor. Thus rated power can be typically produced only up to 130...150 % of the rated name plate speed. Wound rotor synchronous motors can be run even higher speeds. In rolling mill drives often 200...300 % of the base speed is used. Naturally the mechanical strength of the rotor and lifetime of the bearings is also limiting the maximum speed of the motor. It is recommended to consult the motor manufacturer if more than 150 % speed is required by the application.



So in other words, to increase the frequency to a motor, you decrease its torque. This could be a problem for pillar drills ect.
Bear in mind that this descibes an inverter that suplys a motor, and has a ratio of one drive to one motor. Ill do some more digging, to see if you can get one that will alter a whole supply to a building ect.

John
 
I was under the impression the OP wanted to supply USA style outlets in an area with 110V 60Hz. A variable speed drive (often referred to as invertor) would not normally be used for this. This would require a static style invertor to just supply 110V at the 60Hz required.

You are correct in that output torque drops off as the base speed of a motor increases, although most EU motors today are dual rated as 50/60Hz so there would be negligible difference

The guys at Statron should do a static convertor for this Statron: secure power supplies (not on their website but they should do something depending on 1Ph, 3Ph and KVA)
 
Hi guys, nice to see everyone has been busy working the problem whilst I have been away enjoying xmas with the rest of the family.

At the moment he is using a petrol "cube" generator which outputs uk 230/110, and a converter lead with a uk plug on one end and a us socket on the other. As this is running everything ok, I was just going to work out his requirements and source a 230 to 110 transformer to suit.

I have also phoned the council and had a chat with a very helpfull chap there. He said install uk 110 outlets. As long as I comply with uk reg's they will sign it off, Then if the if the person using them makes up his own leads he is responsible not me.
 
Hi guys, nice to see everyone has been busy working the problem whilst I have been away enjoying xmas with the rest of the family.

At the moment he is using a petrol "cube" generator which outputs uk 230/110, and a converter lead with a uk plug on one end and a us socket on the other. As this is running everything ok, I was just going to work out his requirements and source a 230 to 110 transformer to suit.

I have also phoned the council and had a chat with a very helpfull chap there. He said install uk 110 outlets. As long as I comply with uk reg's they will sign it off, Then if the if the person using them makes up his own leads he is responsible not me.

Phone Birmingham Transformers, they will do you a decent wall or floor mount transformer in an air cooled metal case to whatever spec you want

I would go for tapped primary 215, 220, 225,230,235,240, 245,250 Secondary 55-0-55 with an earth screen ( tappings cost nothing extra )

Make sure you use a double pole protective device as the earth is centre tapped

Birmingham Transformers Ltd
 
Last edited by a moderator:

Reply to 110v circuit in workshop. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
393
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
978
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
If it is TT then you can use the armour of any of them as CPC but will almost certainly need an up-front delay RCD at the sub-main feed point to...
Replies
5
Views
961
Given the apparent lack of earth, combined with no short circuit or over current protection, I'd contend that luck has been the sole factor...
Replies
5
Views
611
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top