View the thread, titled "110v consumer unit" which is posted in UK Electrical Forum on Electricians Forums.

bigspark17

-
Arms
Hi, not experienced this before but i have a workshop where the 110v consumer unit (old wylex 3036 board 4way)
Do the board is fed from a 16amp sp mcb from a t0&n board. Then goes into. Standalone transformer wall mounted 3.5kva then into the cu and then to 4x 110v socket outlet.

Ive managed to source a (protek 110v double pole rcd) so i was going to arrange the new consumer unit in this order
2 pole 100amp main switch
30mA 110v 2 pole rcd
4x 16amp mcb
(All protek)

Thankd for any help/guidance
 
110V is really “2 phase” with a centre tapped earth… so only 55V from either phase to earth.

The breakers need to be double pole as there is no earthed neutral on each outgoing circuit for single circuit isolation.
 

Reply to the thread, titled "110v consumer unit" which is posted in UK Electrical Forum on Electricians Forums.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top