Hi

This is my first post and just a little background info I completed level 2 and 3 at college (full time) and have got a job with an electrical contractor in Southampton, I dont think I'm 'properly' qualified until Ive done a couple of years out on site but I'm getting there.

Anyway, I wanted to practice testing etc at home and did earth fault loop impedance on a few of my lights, some tested fine and a few wouldn't test, I flicked the meter on to volts and it was measuring 116v (using 3 lead) so I tested between line and neutral and measured 230v but between line and earth just 60v.

What would cause something like this, I'm guessing a poor earth connection (high resistance) but not certain hence my question?

Thought I'd add to this it was the same with lamp in and out
 
Last edited by a moderator:
Hi DJ, When you connect a 3 lead meter to L-E-N and the E is floating, your meter effective creates a potential divider of equal value impedances across the supply, hence the volt drop across either impedance is approximately half the supply volts and this is what you have measured, 230/2 = 115V, virtually the 116V your meter indicated.
 
what was your dead test, R1R2 or R2 or even your Zs

you may posibly be using the meter wrong, before we can start fault finding.
 

Reply to 116v at lights in the Talk Electrician area at ElectriciansForums.net

Similar Threads

Well at about 9.30 last night I stripped the door card off and found the culprit, cable snapped and end off. So I spent another hour and managed...
    • Like
    • Funny
Replies
2
Views
234
  • Question
Good point James. It would have been nice if the manual had mentioned which of the leads were being used for what though. It simply shows the LNE...
Replies
7
Views
521
  • Question
And exciting when that Hager AFDD finally tripped 😂
2
Replies
28
Views
2K
nicebutdim
N
  • Question
When I did my AM2, I had it drummed into me that I had to follow Guidance Note 3 carefully. So, did you follow the guidance in GN3 for checking...
Replies
1
Views
966

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks