116v at lights

D

DJ Electrician

Hi

This is my first post and just a little background info I completed level 2 and 3 at college (full time) and have got a job with an electrical contractor in Southampton, I dont think I'm 'properly' qualified until Ive done a couple of years out on site but I'm getting there.

Anyway, I wanted to practice testing etc at home and did earth fault loop impedance on a few of my lights, some tested fine and a few wouldn't test, I flicked the meter on to volts and it was measuring 116v (using 3 lead) so I tested between line and neutral and measured 230v but between line and earth just 60v.

What would cause something like this, I'm guessing a poor earth connection (high resistance) but not certain hence my question?

Thought I'd add to this it was the same with lamp in and out
 
Last edited by a moderator:
the voltage readings confused me, 116v using the 3 lead meter, then 60v L-E.

Why was the EFLI meter reading 116v?
 
Hi DJ, When you connect a 3 lead meter to L-E-N and the E is floating, your meter effective creates a potential divider of equal value impedances across the supply, hence the volt drop across either impedance is approximately half the supply volts and this is what you have measured, 230/2 = 115V, virtually the 116V your meter indicated.
 
what was your dead test, R1R2 or R2 or even your Zs

you may posibly be using the meter wrong, before we can start fault finding.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
DJ Electrician,
Last reply from
pblec,
Replies
4
Views
1,135

Advert

Back
Top