its the single phase voltage times the number of phases.

I got this formula off one of the forum pages. I didnt know if it was correct thats why i asked about it. Ive since talked to an industrial electrician who told me its the correct formula to use.

to find the 3 phase voltage from single phase you multiple the single phase voltage by the square root of 3 (1.732) not by 3.
 
Sorry Ian, what are you confused by??

The calc is correct the sum is 15.88A per phase.

So what you are saying that he has a single phase voltage off 400 and a 3 phase voltage of 692 that is what I am saying from your calculation.
 
Last edited:
to find the 3 phase voltage from single phase you multiple the single phase voltage by the square root of 3 (1.732) not by 3.

ian it was the max current per phase i was after not the phase to phase voltage but thanks anyway.
The formula i found must be a rule of thumb or something cos it works out just about the same as the formula lenny gave.
thanks for the input.
 

Reply to the thread, titled "11kVA 3 phase supply" which is posted in Electrician Talk | All Countries on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Daily, weekly or monthly email

Back
Top