The same loony who surprises you with an 11 kw range oven with induction hob, warming draw twin oven and grill after saying its a double oven and gas hob......

Bit of 6mm and a 32 it is, then. ;)
 
6mm clipped direct just on the limit, but you'd need a OCPD of 50A, so 6mm is out of the equation.
Why?
433.3.1 (ii)
A shower is a fixed resitive load, so very unlikely to be subject to overload current apart from a fault.
It has fault protection via the RCD (and the 50A CB), any fault will be cleared in less than 0.3 seconds that the RCD takes, so a 50, or even 100A CB will be compliant.
(of course so long as cable length, Zs, grouping/reference all comply too)
 
the shower is 47A so the OCPD needs to be >47A but less than the Iz of the cable. so a 50A MCB. this means that the cable Iz must be > 50A so it's got to be 10mm.


what's the RCD got to do with overload protection?
 
433.3.1
There is no need for circuit protection if the load is unlikely to carry overload currents. A shower will not overload unless it has a fault. No-one is likely to fix the circuit directly to the outgoing RCD terminals, so fixing it to a CB rated higher than the current carrying capacity of the cable is quite acceptable in such circumstances, so long as the cable can carry the current of the appliance.
A L-N fault will cause many hundreds of amps to flow (in most installations), meaning any CB fitted, whether 50 or 100A will trip virtually instantly. It is only in fault conditions that a L-N short will occur.
Hence it is compliant to run a cable with a 47A capacity, feeding a 45A fixed load appliance, fed via a 50A CB, as there will be fault protection, both via any CB fitted, and via the RCD which will have to be fotted in any domestic premises. There will be no overload protection, but that isnt required, as stated in 433.3.1.
 

Reply to 11kw shower cable size? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
333
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
859
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
985

Similar threads

Being pedantic, the Crabtree 50A cooker switch is a 4500/1, which has 'cooker' printed on it. For a shower, you require the 4500, which is the...
Replies
3
Views
336
  • Question
It’s a single phase 1500w motor. It has a 6 amps speed controller, distance from controller to fan about 3-4 meters .
Replies
7
Views
805

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top