C
Chris14
For 11kw shower what cable size is required for 15m run?
greasy monkeys perhaps:joker:Who in their right mind would want an 11kw shower?
Who in their right mind would want an 11kw shower?
The same loony who surprises you with an 11 kw range oven with induction hob, warming draw twin oven and grill after saying its a double oven and gas hob......
Bit of 6mm and a 32 it is, then.![]()
A 9kw is just as good at getting the grease out of a monkeys fur and i would knowgreasy monkeys perhaps:joker:
Why?6mm clipped direct just on the limit, but you'd need a OCPD of 50A, so 6mm is out of the equation.