Eve Chaps,
Went to look at a house extension today and put my meter on the sockets and lights.
I found that I had 124v on the earth but no tripping.
When I touched the terminal I got no shock etc.
Any ideas ?
split the earths from the CU one at a time to locate which circuit has the fault. then investigate that circuit. continuity, IR etc. etc. could be a crossesd N/E
bot the N and E are connected all together in the CU. dis each cpc in turn to trace fault to 1 circuit. then dead test that cct.
Reply to 124 volts on earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Only the N side of the lamp would be at 0v if you went further along the element the voltage would rise.
Exactly. I was going to ask on the earthing once he clears this boiler fault (suspect on internal component). OP mentions oil boiler but makes no...