I found the circuit at fault (lighting)

I also pulled breaker for the lighting and was ok but it also took power of 3 sockets
that tells me there's some serious problem with how it's been wired.
 
the earth would have to be missing from near to the cu end of the circuit. what is more worrying is that by isolating lights, you are losing power to 3 sockets.
 
trying not to over complicate.

2 possible causes

1, Earth leakage on a class 1 appliance

2, Crosse cpc and N

the first sould be easy enough to eliminate, and the second im afrais you are going to have to trace the circuit a leg at a time investigating every outlet and junction
 
Sorted the sockets out but still Cant find this problem grrrrrrrrrrrrrrrrrrr agggggggghhhhhhhhhhhhhhhhhhhhhh

Also found no earth on water ooooooooo errrrrrrrrrrrrrr

Do you think some cable some place is crushed and this is y its getting the voltage ?
 
If its a TNCS system i think youll find that the problem is a faulty or missing neutral do some R2& Rn tests check the Ze at the board
 

Reply to 124 volts on earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
706
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Only the N side of the lamp would be at 0v if you went further along the element the voltage would rise.
Replies
14
Views
910
Exactly. I was going to ask on the earthing once he clears this boiler fault (suspect on internal component). OP mentions oil boiler but makes no...
2
Replies
19
Views
789

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top