Hi Gents
Client requirement is for 125 kVA Distribution Board,
What does it mean ?
amps when KW is known (3 phase calc shown). 125kva is 100KW
kW x 1000
1.73 x E x PF
E is the voltage(400) and PF around 0.8
I get 180A per phase max
Amps where KVA is known
kVA x 1000
1.73 x E
Or single phase
kVA x 1000
E
=543A.
Correct me if I'm wrong
It’s 180A at 400V.
But now I’m going to ask a serious question. Are you competent to undertake this?
To ask the question in the first place would suggest not. I’m sorry but it’s not aunties fuse board under the stairs.
Reply to 125 kVA Consumer Unit in the Australia area at ElectriciansForums.net
I've a (large, with private water treatment, ground source heating, workshops....) house I built in Devon many years ago - by the 'add it all up'...