tom20
Hi,
We are undertaking quite a big job for an extension at a school and as it is a little out of our experience i was hoping to run it by a few of you kind folk before we have another meeting with the client on Tuesday.
I've read through the forum at cable calc questions and i know they can come across a little lazy! so i will show as much info and what i have come up with so far.
The job is an extension for a new kitchen / dining room at a school and the client require a new 125 kva supply. XLPE/LSF/SWA/LSF 4core with separate earth underground in a 150mm duct. the run is to be 300m from a sub station located on the edge of the grounds.
We have so far come up with 180A required (per phase?) with 5% volt drop Which brings us to requiring a 95mm 4core swa cable.
does this seem correct? or a little too excessive? and lastly what would be expected in terms of terminating this in the new intake room before MCCB main dist board
Thank in advance and please let me know any other info required.
tom
We are undertaking quite a big job for an extension at a school and as it is a little out of our experience i was hoping to run it by a few of you kind folk before we have another meeting with the client on Tuesday.
I've read through the forum at cable calc questions and i know they can come across a little lazy! so i will show as much info and what i have come up with so far.
The job is an extension for a new kitchen / dining room at a school and the client require a new 125 kva supply. XLPE/LSF/SWA/LSF 4core with separate earth underground in a 150mm duct. the run is to be 300m from a sub station located on the edge of the grounds.
We have so far come up with 180A required (per phase?) with 5% volt drop Which brings us to requiring a 95mm 4core swa cable.
does this seem correct? or a little too excessive? and lastly what would be expected in terms of terminating this in the new intake room before MCCB main dist board
Thank in advance and please let me know any other info required.
tom