Hi all, good afternoon.
New on here, so here goes!
Quick question and some advice really!
I have a 12KW three phase immersion heater installed into a hot water cylinder (for commercial premises).
The immersion heater enables and disables via an on site building management system so therefore the immersion heater enables via a Schneider (3ph) ICT 25A 400v contactor. Complete with 230v coil.
The building in question (their maintenance man) is explaining to me that he thinks the contactor is 'under rated' as the 12KW immersion heater will be drawing more load?? Also he seems to think the contactor is changed every 12 months or so??
above the contactor there is a Schneider (3ph) C60HB B20 415v MCB installed.
What kind of load 'potentially' could a 12KW three phase immersion draw? Is it simple ohms law?
12000 watts (12KW) / 400v = 30 amps or is there (back to my college days) a route3 equation in there somewhere + a power factor? I feel a clip on clamp meter coming on soon!
Feedback appreciated
Thanks
New on here, so here goes!
Quick question and some advice really!
I have a 12KW three phase immersion heater installed into a hot water cylinder (for commercial premises).
The immersion heater enables and disables via an on site building management system so therefore the immersion heater enables via a Schneider (3ph) ICT 25A 400v contactor. Complete with 230v coil.
The building in question (their maintenance man) is explaining to me that he thinks the contactor is 'under rated' as the 12KW immersion heater will be drawing more load?? Also he seems to think the contactor is changed every 12 months or so??
above the contactor there is a Schneider (3ph) C60HB B20 415v MCB installed.
What kind of load 'potentially' could a 12KW three phase immersion draw? Is it simple ohms law?
12000 watts (12KW) / 400v = 30 amps or is there (back to my college days) a route3 equation in there somewhere + a power factor? I feel a clip on clamp meter coming on soon!
Feedback appreciated
Thanks