12v cable lengh/csa
when installing 12v lights how do you calulate the csa/cable length ?
i know that a 50w lamp would pull 4.16a @ 12volts so cable sizes have to be larger,
but how would you calcuate the maximum length of that cable? assuming your using twin and earth clipped direct ?
thanks in advance
Usually the transformer would be local to the fitting, so you'd calculate the cable size based on 230v and let the manufacturer worry about the 12v part.
How come you're doing it this way?
volt drop works the same way at 12volts as it does at 240volts. it's still mV/A/m as in the tables, app.4.
so to work out the volt drop you 1st find out the mV/a/m for the cable, 2.5 = 15 (pg 275 brb) times this value by Ib which would be 50 watts (4.16 amps) then times by how many meters say 6 then divide by 1000
15 x 4.16 x 6 / 1000 = 0.3744
i think to 3% rule for lighting only applies to 230v. it's not going to make any difference to 12v lighting.
We tested an installation a while ago and the ELV lighting had been done through 250VA transformers, each feeding 5 downlights.
The runs varied between 1 and 10 metres and the fittings on the longer runs were so much dimmer than the rest!
The moral is to keep the 12V run to an absolute minimum, it's trouble!
chrisreid186,
Adam W,