Hello,

I am wondering if this is allowed, I dont have a big need to do such a thing, just would like to know how it would stand up with the law and regs etc

If you have a class 1 (or class 2 for that matter) light fitting and you wanted to convert it to 12v to make it PELV, for use in an old house with no CPC in lighting circuit or in a special location etc

It is very easy to do, as B22 and E27 bulbs come in a range 12v versions (typically used for boats or motorhomes). So swap the bulb and then supply it via a safety isolation transformer of correct voltage and label up appropriately, after checking wiring is appropriate for the current at 12v + overcurrent protection on 12v side

I am thinking that there could be a problem with this as the light fitting was sold as a 230v fitting and therefor tested to be exactly that, however by you changing the voltage would you in effect be liable for any faults with that light whether it is the fault of the 12v or not and the like

Thanks Marcus
 
if you were using a fitting at a voltage above it's rated capacity, it could be a problem. reducing the voltage can't cause any trouble as long as you allow for the fact that the current is 20 X @ 12V as it is @ 240V.
 
if you were using a fitting at a voltage above it's rated capacity, it could be a problem. reducing the voltage can't cause any trouble as long as you allow for the fact that the current is 20 X @ 12V as it is @ 240V.

yes thats my thinking of course would need to be labeled up and wire size checked

how would commission such a thing although, what would be on the cert
 
If I was doing this I'd probably choose 36V. As mentioned above the current drawn would be large quite large at 12V and the volt drop would be a problem. Bit easier now with LED though. Certainly unconventional, would need a really really good reason to avoid rewiring the circuit.
 
I see your point with the voltage, although with LED bulbs now which draw so little it can be achieved easily.

yes like you say in most cases you would run a new cpcs in or use appropriate double insulated or PELV fittings

could be handy of there were some nice looking class 1 outside lights on a PME supply on easy reaching distance of say a hot tub on TT
 
If the circuit/s do not incorporate cpcs how will you earth the isolating transformer.

Good point!

As i understand it requires and earth in the regs incase of insulation fail and therefore not electrically separated. Is this still the case with a safety isolation transformer with extra insulation.

I guess the fact its extra low voltage doesn't negate the eend for earth
 
It is possible you can get an encapsulated transformer which is Class II however it's point of connection is likely to require a cpc. It should be noted Class II protection in a dwelling is not realistically practical as it is not under the supervision of skilled persons.
 
If the problem is the lack of CPC in the lighting circuits, and the current for 12V (or 24V, whatever) is within the rating of all existing cable/switches/sockets, then the only issue for earthing would be any electrostatic shield (if output floating, probably a bad idea) or the secondary winding for the isolation transformer.

But that transformer could be near the existing CU so all cables for lighting (without CPC) are just moved over to the low voltage supply, and the transformer is earthed at the CU location by whatever means necessary.
 
If the problem is the lack of CPC in the lighting circuits, and the current for 12V (or 24V, whatever) is within the rating of all existing cable/switches/sockets, then the only issue for earthing would be any electrostatic shield (if output floating, probably a bad idea) or the secondary winding for the isolation transformer.

But that transformer could be near the existing CU so all cables for lighting (without CPC) are just moved over to the low voltage supply, and the transformer is earthed at the CU location by whatever means necessary.

I do like that thinking, would mean you wouldn't need to run a CPC in

However still not sure if it acceptable to change 230v fittings to a lower voltage, would that in effect make you the manufacturer
 
If you are simply installing standard lamps that are low voltage and below the current limit for the fittings I don't see any problem. The main issue has already been mentioned, that the current will be 20x or so, and that would be the issue that would bother me.

But still, a 12W LED bulb is much the same brightness as a 100W tungsten lamp and while it draws 1A at 12V, you don't have the additional 88W of heating to worry about!
[automerge]1587160863[/automerge]
NOTE: I have not checked that 12W 12V LED bayonet bulbs actually exist...
 

Reply to 12v conversion of 230v light fitting. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Thank you for your reply. I manage to find the issue I think, the natural and live wasn't inserted properly in one the wago Further down causing...
Replies
2
Views
878

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top