i do but just didnt understand exactly, and if i new the answer i wudnt have asked wud i !!
 
aaelectric
The information below is the table in the OSG that summarises the requirements, this is very basic information that is readily available.

The fixed permanently connected equipment, including ventilation equipment and luminaries, allows the items you are asking about in zones 1 and 2 (although the source of supply for SELV items must be outside zones).

Extract fans should have a means of local isolation for maintenance, although this can be the MCB for the circuit, and it is common practice to fit a fan switch, it is more likely that the manufacturers instructions will require an isolator switch and Manufacturers instructions take precedence.

Table 8.1
701.32 701.5
Requirements for equipment (current-using and accessories) in a location containing a bath or shower
Zone
Minimum degree of protection
Current using equipment
Switchgear and accessories
0
IPX7
Only 12 V a.c. rms or 30 V ripple-free d.c. SELV, the safety source installed outside the zones.

None allowed
1
IPX4 (IPX5 if water jets)
25 V a.c. rms or 60 V ripple-free d.c. SELV or PELV, the safety source installed outside the zones.
The following mains voltage fixed, permanently connected equipment allowed: whirlpool units, electric showers, shower pumps, ventilation equipment, towel rails, water heaters, luminaires
Only 12 V a.c. rms or 30 V ripple-free d.c. SELV switches, the safety source installed outside the zones.

2
601-08-01
601-09-03
IPX4 (IPX5 if water jets)
Fixed permanently connected equipment allowed. General rules apply.

Only switches and sockets of SELV circuits allowed, the source being outside the zones, and shaver supply units complying with BS EN 61558-2-5 if fixed where direct spray is unlikely
Outside zones
601-08-01
No requirement
General rules apply.
Accessories allowed and SELV socket-outlets and shaver supply units to BS EN 61558-2-5 allowed. Socket-outlets allowed 3 m horizontally from the boundary of zone 1
 

Reply to 12v fan in bathroom in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
124
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
910
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Which begs the question, where does the second brown wire come from?
Replies
5
Views
434
My money is on the capacitor dropper. The relay isn't getting the power to latch on. Tapping the unit will 'bounce' the relay into it's on state...
Replies
9
Views
477

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top