Hi Everyone
So i've installed my first kitchen and everything has gone well. I've wired in the oven based on a sparkies recommendation but I just want to check I've done things correctly and try to understand a bit more about cooker circuits.
The oven is a single NEFF fan oven 2.9kW . There are no other ovens in the kitchen, and just a gas hob. The previous kitchen that had been installed in the last few years has a dedicated cooker switch which goes back to the circuit board on it's own dedicated fuse. Next to this fuse is a shared 30A RCD which covers the oven, ground floor lighting, sockets etc. A socket is spurred off of the cooker switch and is controlled by it. It is at the back of the oven unit.
2900W / 230V = 12.6Amps. So I put some 2.5mm flex on the oven with a 13A plug, and plugged it into the spurred socket. I'm pretty sure this is what the sparkies recommended to me.
Based on this I've got a few questions I hope someone can help me with.
1) Is this safe / correct setup, and do I need to have it certified and tested by an electrician?
2) I can see that you want a fuse as close as possible to the maximum rating of an applicance, but just out of interest what could happen if you put a 12.6A cooker on a 30A fuse? For example, if there was a fault in the oven, could it get hotter and hotter and hotter and start a fire before it tripped out at 30A?
3) Both sparkies I spoke to said to use 1.5mm flex on the oven. But I thought this was only rated up to 10A? I put a 2.5mm cable on there in anycase which I believe is rated to 13.5A, but a 1.5mm would have been a lot easier to wire into the plug.
Many thanks. Looking forward to your responses
So i've installed my first kitchen and everything has gone well. I've wired in the oven based on a sparkies recommendation but I just want to check I've done things correctly and try to understand a bit more about cooker circuits.
The oven is a single NEFF fan oven 2.9kW . There are no other ovens in the kitchen, and just a gas hob. The previous kitchen that had been installed in the last few years has a dedicated cooker switch which goes back to the circuit board on it's own dedicated fuse. Next to this fuse is a shared 30A RCD which covers the oven, ground floor lighting, sockets etc. A socket is spurred off of the cooker switch and is controlled by it. It is at the back of the oven unit.
2900W / 230V = 12.6Amps. So I put some 2.5mm flex on the oven with a 13A plug, and plugged it into the spurred socket. I'm pretty sure this is what the sparkies recommended to me.
Based on this I've got a few questions I hope someone can help me with.
1) Is this safe / correct setup, and do I need to have it certified and tested by an electrician?
2) I can see that you want a fuse as close as possible to the maximum rating of an applicance, but just out of interest what could happen if you put a 12.6A cooker on a 30A fuse? For example, if there was a fault in the oven, could it get hotter and hotter and hotter and start a fire before it tripped out at 30A?
3) Both sparkies I spoke to said to use 1.5mm flex on the oven. But I thought this was only rated up to 10A? I put a 2.5mm cable on there in anycase which I believe is rated to 13.5A, but a 1.5mm would have been a lot easier to wire into the plug.
Many thanks. Looking forward to your responses