Can anyone see anything wrong with two double 13A sockets wired with 20m of 6mmsq SWA protected by a 50A RCBO. Normally I'd max radials at 32A, but the client has 4x 10A loads.
Since the 13A socket on a cooker supply is generally protected by around 40-50A I am guessing it's fine.
NO THEY ARE NOT, the fusing in the plug top could allow over 26A to be drawn from a single twin s.o.
Look up the characteristics of the standard 13A plug top fuse, see how muhc current it will pass without "blowing", then multiply that by two to see what you are expecting the s.o. to take.
As I understand the testing, standards etc. of a standard twin 13A s.o. from a professional standpoint this is an overload situation.
A SINGLE 13A load in a twin s.o. OK, 2 10A loads need to be checked.
The plug top fuses WILL NOT protect the s.o. how can they as they are downstream.
Paul
Thanks for resposes so far.
More info:
SWA will be clipped direct.
The tables give 62A for 6mmsq (volt drop 7.9v)
The MK double sockets are rated to 13A per socket.
As far as I can see this still should be okay.
Paul as the fuse limits th load that is able to be drawn by the cable to the appliance it also limits the load drawn from the downstream supply.
It is this reason that on larger installations 25mm cables can be taken from 300A busbars to 63A isolators as long as ther within 3 metres as th 63A protection is less than the maximum CCC of the 25mm cable.
have a look at Reg 434.2.1 .
BS7671 is irrelevant here, you MUST refer to BS1363 for the allowable socket loads.
I am aware of the scenarios you suggest however, they have no relevance in the OP scenario.
Under the situation of small overloads of long duration what summated current could be drawn by 2 off 13A fuses without them "blowing"?
Paul
I once ( temporarily) put an immersion off a plug top thinking that 13A is ok, and it got very hot, so the moral of the story is don't take ratings in to account, common sense is more valuable.
The only thing I would say is it's not recognised as a standard circuit in appendix 15 of BS7671 for ring and radial final circuit arrangements so you may have to note it as a departure.
Reply to 13A sockets on 50A RCBO in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Nope, totally fubar.