Can anyone see anything wrong with two double 13A sockets wired with 20m of 6mmsq SWA protected by a 50A RCBO. Normally I'd max radials at 32A, but the client has 4x 10A loads.

Since the 13A socket on a cooker supply is generally protected by around 40-50A I am guessing it's fine.
 
NO THEY ARE NOT, the fusing in the plug top could allow over 26A to be drawn from a single twin s.o.
Look up the characteristics of the standard 13A plug top fuse, see how muhc current it will pass without "blowing", then multiply that by two to see what you are expecting the s.o. to take.
As I understand the testing, standards etc. of a standard twin 13A s.o. from a professional standpoint this is an overload situation.
A SINGLE 13A load in a twin s.o. OK, 2 10A loads need to be checked.
The plug top fuses WILL NOT protect the s.o. how can they as they are downstream.
Paul
 
Thanks for resposes so far.

More info:
SWA will be clipped direct.
The tables give 62A for 6mmsq (volt drop 7.9v)
The MK double sockets are rated to 13A per socket.

As far as I can see this still should be okay.
 
Paul as the fuse limits th load that is able to be drawn by the cable to the appliance it also limits the load drawn from the downstream supply.
It is this reason that on larger installations 25mm cables can be taken from 300A busbars to 63A isolators as long as ther within 3 metres as th 63A protection is less than the maximum CCC of the 25mm cable.
have a look at Reg 434.2.1 .
 
Last edited:
BS7671 is irrelevant here, you MUST refer to BS1363 for the allowable socket loads.
I am aware of the scenarios you suggest however, they have no relevance in the OP scenario.
Under the situation of small overloads of long duration what summated current could be drawn by 2 off 13A fuses without them "blowing"?
Paul
 
I once ( temporarily) put an immersion off a plug top thinking that 13A is ok, and it got very hot, so the moral of the story is don't take ratings in to account, common sense is more valuable.
 
The only thing I would say is it's not recognised as a standard circuit in appendix 15 of BS7671 for ring and radial final circuit arrangements so you may have to note it as a departure.
 

Reply to 13A sockets on 50A RCBO in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
318
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
297
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
361

Similar threads

  • Question
Nope, totally fubar.
2
Replies
15
Views
2K
  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top