I want to purchase a 10 socket multiplug extension that's 13amps. Does that mean I cant go above 13amps on the whole 10 sockets? I'm thinking even if i put 4 3amp plugs on it I can't use the other 6 so seems pointless having 10.

Tia
 
I want to purchase a 10 socket multiplug extension that's 13amps. Does that mean I cant go above 13amps on the whole 10 sockets? I'm thinking even if i put 4 3amp plugs on it I can't use the other 6 so seems pointless having 10.

Tia
The reason of the 13Amp limitation is that the plug you plug into a socket outlet to feed the multiplug extension will have a Max loading of 13 Amps governed by the 13Amp fuse in this plug top.
The safest option I can advise you to do, is to get some extra 13Amp Socket outlets installed at the point of usage, extension leads, in my opinion are a last resort, and are subject to damage, and will be a fire hazard if left coiled up, during use.
 
Is this the same project as your other post?

For this, I would consider having a dedicated circuit installed for the equipment you mentioned.

FYI.
A peice of equipment with a 5A fuse does not run at 5A. It’s just a step down fuse so if there is an overload, the 5 will pop before the 32A in the consumer unit. (Or whatever it is. May be a 16A radial for all I know)
 
Is this the same project as your other post?

For this, I would consider having a dedicated circuit installed for the equipment you mentioned.

FYI.
A peice of equipment with a 5A fuse does not run at 5A. It’s just a step down fuse so if there is an overload, the 5 will pop before the 32A in the consumer unit. (Or whatever it is. May be a 16A radial for all I know)
Yes same project but scrapping the idea of connecting 2 extensions to each other and just stick to the 1 extension that I found long enough.
 
It doesn’t matter. If I understand the situation, you have a plug in extension lead running from the house. That lead will have a 13amp fuse in its plug.
that’s the limit of what you can run at any one time.
nothing you have mentioned uses a high degree of power. You haven’t mentioned electric heating, or anything like that.
Have a look at the running current for each device. There should be a label, of it will be in the manual. Add the loads together.
I will be verysurprised if you anywhere near 13amp.
 
The Kaoss pad and the MiniNova will each use around 0.25A. The monitor and synth maybe 0.5-1A each, average PC and sound system 1-2A each. I would expect your total load to be around 5-6A for everything, well within the 13A maximum.

One other factor to note when connecting many small items via one 13A plug is the total earth leakage. It should not be allowed to exceed 3.5mA, to limit the risk in the event of the earth connection in the plug coming loose. These six items won't reach 3.5mA, but a system containing 30 small power supplies each using 0.25A, although well within the available 13A load, might do so.
 
I've also seen domestic extension reels which are only rated at 5A - great when someone puts a 13A fuse in the plug!

When coiled into the reel you have a very large inductor and are trying to pump a lot of current through it. It heats up enough to melt the insulation on the cable. Been there, done that...

I would never buy a wind up cable reel since then (about 40 years ago) - although I understand its limitations the rest of the family don’t.
 
When coiled into the reel you have a very large inductor and are trying to pump a lot of current through it. It heats up enough to melt the insulation on the cable. Been there, done that...

I would never buy a wind up cable reel since then (about 40 years ago) - although I understand its limitations the rest of the family don’t.

Yes, very few people fully unwind them.
 

Reply to 13amp multi plug extension? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
299
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
282
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
355

Similar threads

The same socket can be used for different appliances, such as kettles... which will draw more than 5A The size of the cable determines how much...
Replies
4
Views
823
I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

  • exceeding voltage drop
    The cable is way undersized. If the voltage drop is detrimental to the installation I would make...
  • TT advise
    OK My take on the precautions to implement when omitting an up front RCD on a TT system. Tails...
  • SIL vs ATEX
    Good morning all, I have a question for those who are CompEx and SIL aware - I have various Ex...
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top