S

sedgy34

so i went to some apartments (refurbed) to have a look at installing solar on the building roof and noticed at the mains there is no kmfs for the distribution circuit feeding each DB and runs vary from 15 meters to 40 meters, its pretty tight in there and the domestic installer sparky didnt know you have to protect the cables over 3 meters. I asked him have a look in the regs or speak your nic guy he says i dont know who he is and ive been with them 8 years. You could also tell he as lost interest as hes been on it 6 months on his own.
so there is for each 25mm tails to 100a main dp switch coming out in 16mm tails to adaptable box through crimped onto 16mm armoured going outside in a trench length of run 15 to 40 meters, to DB.

your thoughts please
 
KMF's it is then!,
Or you could replace those dappy boxes with wylex metalclad switchfuses with 60A fuses in. Much easier then b*st*rd KMF's!

i did mention i was only there to have a look at installing 4 x4kw solar systems
the domestic installer has done the works on the apartments whilst i popped my head in the mains cuboard to see if there was any room for some inverters. [ElectriciansForums.net] 15 apartmentsthought i would take a sneaky pic
 
i did mention i was only there to have a look at installing 4 x4kw solar systems
the domestic installer has done the works on the apartments whilst i popped my head in the mains cuboard to see if there was any room for some inverters.View attachment 13482thought i would take a sneaky pic

Wiring looks nice and tidy to the meters at the bottom of pic then i scroll up.........
WTF ? lol
Maybe a nice piece of 4 inch tray might help and what the hells going with the earthing thats flapping around in the wind ?
Looks like someones out of their depth to me lol.
 
You could use rear entry redspot fuse holders mounted to the lids of those adap. boxes to fuse the live down to the installad rating of the armoured's, then the installation becomes compliant.
 

Reply to 15 apartments in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
817

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
487
  • Question
Yeh that’s my thinking. I have to supply the box so can order a bigger 3 phase option to give myself a bit more room
Replies
3
Views
846

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top