I just got a job to connect a 15 KW motor up. The run is 40 meters and to my calcs I could get away with 6mm armoured but that's with a volt drop of 9.6 volts! Just after a few opinions as to if I should run the 6mm or just go for a 10mm? The cable will be clipped direct. Cheers fellas.
 
Ok so working out 3 phase current is slightly different to single phase


The calc is P/(V x root3 x power factor)

which gives in your case 15000/(400 x 1.732 x 1) (assuming a power factor of unity although around 0.85 is more accurate

= 21.65A per phase. Even at 0.85PF it's only a shade over 25A.

So your cable needs to be able to carry a minimum of 25.65A under it's normal service conditions, assuming 0.85PF.

I would use 6mm SWA protected by a 32A C curve MCB.


Edit....in addition your max VD would be 5% of 400V = 20V, so your 9.6V is fine.
 
Last edited by a moderator:
Its a compressor. It already has a flex coming out of it with l1 l2 l3 and an earth so all the starter is internal. I'm just gona run the cable and put an isolator up.
 
Its a compressor. It already has a flex coming out of it with l1 l2 l3 and an earth so all the starter is internal. I'm just gona run the cable and put an isolator up.

hi
if you do end up connecting it up make sure you check the rotation of the motor, when i first started i did a similar job to yours and when i ran the compressor it all worked great untill the fly wheel came flying off causing £100 worth of damage!...gutted. hope this is of use to you

regards
gary
 
hi
if you do end up connecting it up make sure you check the rotation of the motor, when i first started i did a similar job to yours and when i ran the compressor it all worked great untill the fly wheel came flying off causing £100 worth of damage!...gutted. hope this is of use to you

regards
gary

Going off the thread a little so excuse me


Now that is some sound advise for trainees and some sparks who rarely touch 3 phase jobs

It should be written into your brain as essential things a spark should remember to do


If you dont wire and connect 3 phase motors and want to be assured if you did so ,a little question for you
What would you do if it was reversed?
 
Fellas it was a nightmare today lol. Firstly the 32Amp C breaker kept tripping so I rang the manufacturer and they said I needed at type D! By this time it was 4 o'clock and I was giving up hope. Luckly a wholesaler came through and I quickly connected it up to my horror I found that the compressor was running the wrong way! I read the instructions and it said that an LED will come on if the motor is in reverse so I left the motor for 2-3 mins and the nosie wasnt better so I shut it off and rang the manufacturer where they told me the LED dont work and I should never believe screen readouts. Luckly the belts had come off the pulleys so there was no major damage but just be warned anyone connecting a compressor, if you think the rotation is wrong then stop the motor and try the other way! All sorted now thank god!
 
Fellas it was a nightmare today lol. Firstly the 32Amp C breaker kept tripping so I rang the manufacturer and they said I needed at type D! By this time it was 4 o'clock and I was giving up hope. Luckly a wholesaler came through and I quickly connected it up to my horror I found that the compressor was running the wrong way! I read the instructions and it said that an LED will come on if the motor is in reverse so I left the motor for 2-3 mins and the nosie wasnt better so I shut it off and rang the manufacturer where they told me the LED dont work and I should never believe screen readouts. Luckly the belts had come off the pulleys so there was no major damage but just be warned anyone connecting a compressor, if you think the rotation is wrong then stop the motor and try the other way! All sorted now thank god!


most three phase equipment will have an arrow on a pulley to show correct rotation check before running. I always try to find this and flick the starter to check rotation. Some large compressors and other equipment will be wrecked running in reverse. most submersible three phase pumps have an arrow to show the direction the pump will try to turn (reaction direction) when the starter is momentarily flicked.
 

Reply to 15 KW motor to connect in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

Ask your electrician when they do a site visit as to what is required they can also notify the installation to Building Control under Part P of...
Replies
1
Views
384
Sorry i think i may have confused the situation - "relay" is a general term in this context. The starter "relay" nowadays is usually located...
Replies
11
Views
1K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
1K
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
3K
For the cable run, what is the allowed % voltage drop between the MCC and the pump?
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks