Why are 16, 32 and 63 amps used as an MCB rating instead of 15, 30 and 60 amps? Best theory that I can come up with was when the UK switched to 230 volts this was to make up for the drop in voltage but have noting to back that up.

Here are the ratings I'm familiar with:

View: https://Upload the image directly to the thread.com/a/trtK7pI


The nominal voltages which go along with them:

View: https://Upload the image directly to the thread.com/NFO74Tp
 
The way it was explained to me is that the series of values aids in coordination and discrimination between breakers.

If you take the series
16, 20, 25, 32, 40, 50, 63, 80, 100
then from each point, if you go up TWO steps, then that value is ~1.6x where you started, and your downstream breaker should now reliably trip before the upstream.


IF you're in the thermal region, right?
 
Yes, the thermal curves provide selectivity, but once you hit the magnetic trip there is very little.

But for fuses it is generally OK for BS88 style at a 1:1.6 sort of ratio, but to be sure you would normally go for a 1:2 ratio. For example, if you have a 80A DNO fuse then a 40A fuse-switch to feed something (out building DB, whatever) then wherever happens on the end of that won't take out your main supply.

Getting selectivity MCB to fuse is hard as well, but often if you have a 1:2 ratio and B-curve you get a usable level, e.g. 20A B-curve & 40A fuse is going to be to PFC of around 900A which, depending on cable length, might never be reached so the fuse lives past a MCB trip on a hard fault.
 
Yes, the thermal curves provide selectivity, but once you hit the magnetic trip there is very little.

But for fuses it is generally OK for BS88 style at a 1:1.6 sort of ratio, but to be sure you would normally go for a 1:2 ratio. For example, if you have a 80A DNO fuse then a 40A fuse-switch to feed something (out building DB, whatever) then wherever happens on the end of that won't take out your main supply.

Getting selectivity MCB to fuse is hard as well, but often if you have a 1:2 ratio and B-curve you get a usable level, e.g. 20A B-curve & 40A fuse is going to be to PFC of around 900A which, depending on cable length, might never be reached so the fuse lives past a MCB trip on a hard fault.


Good to know.

RK-1 and RK-5 fuses will achieve 100% selective coordination up to 200,000 amps provided a 2:1 ratio.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Earth

Thread Information

Title
16, 32 and 63 as a rating
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
17
Unsolved
--

Advert

Thread statistics

Created
Cookie,
Last reply from
Cookie,
Replies
17
Views
2,487

Advert

Back
Top