Why are 16, 32 and 63 amps used as an MCB rating instead of 15, 30 and 60 amps? Best theory that I can come up with was when the UK switched to 230 volts this was to make up for the drop in voltage but have noting to back that up.

Here are the ratings I'm familiar with:

View: https://Upload the image directly to the thread.com/a/trtK7pI


The nominal voltages which go along with them:

View: https://Upload the image directly to the thread.com/NFO74Tp
 
The UK never changed voltage.

We had 240/250V as nominal with an allowance to go down a bit and over a tiny bit.

Now we have 230V with an allowance to go up a bit and down a tiny bit.

They are essentially the same voltage range, so in terms of practical changes the UK didn't change.

R'10 preferred values are now used right throughout the industry, unfortunately ratings have only partially moved (6A doesn't fit the series it should be 6.3A, 45A shouldn't fit only fits in R20, R'20, R''20 and so on series )
 
Many different voltages were in use in different areas, from 100 to 250, even different frequencies (and DC) before the national grid standardised all new supplies from around 1931 onwards. The highest voltage in normal use was 250V, so most single-phase accessories were rated for that voltage, and most 3-phase equipment for 500V.

The majority of supplies were 200V or higher, therefore 5A was usually sufficient for 1kW and the 5A multiples approximately corresponded to the kW rating of typical loads.

Typical domestic applications were:
5A - lighting, small outlets
10A - heating, fell out of favour in the 1930s
15A - heating, water heating (stored), large domestic outlets
20A - radial circuit for small numbers of BS1363 outlets and FCU-attached appliances (after 1947)
30A - cooking, ring final circuits for BS1363 outlets (after 1947), main fuses for small installations
45A - large cooking, submains, showers (not then popular)
60A - main fuses

The UK was quite old-fashioned in terms of OCPD choice, we continued to favour rewireable fuses when Europe was increasingly using HRC cartridges. Fuse wire was sold in the above ratings and these were carried over to HRC fuses when we started to get into those. You can still buy cards of fuse wire in hardware stores, with the most popular domestic ratings, 5, 15 & 30A and sometimes 20A.

As the popularity of MCBs increased the first really successful product series also used the multiples of 5A e.g. Crabtree C50 (that's a model number, not a rating), Wylex plug-in and NB types, MK LN / Sentry and other early BS3871 models. We migrated to the Renard number ratings with the rest of Europe in the 1980s. Series that were current at the time existed in both flavours. E.g. MK Sentry Mk.1 can be found with 5A, 6A, 10A, 15A, 16A etc ratings. Many products such as industrial switchgear also made the shift (30-32A, 60-63A etc) with the same basic products being rebadged with the new rating, perhaps with a styling facelift.
 
Did some Voltage warnings signs diminish as well ?
 

Attachments

  • [ElectriciansForums.net] 16, 32 and 63 as a rating
    Not-too--long-ago.png
    604.8 KB · Views: 37
when the UK switched to 230 volts this was to make up for the drop in voltage but have noting to back that up.

The UK didn't switch to 230V anywhere but on paper, the national grid didn't magically change voltage overnight, all of the final substation transformers stayed right where they were with a 250/433 output.

Also increasing fuse rating to coincide with a reduction in voltage wouldn't make sense, generally the overall effect would be a slight reduction in load current for the majority of cases.
 
Also increasing fuse rating to coincide with a reduction in voltage wouldn't make sense, generally the overall effect would be a slight reduction in load current for the majority of cases.

I see it like this-

15 x 240= 3,600 va

16 x 230= 3,680 va

Although that assume the load will actually be rated 230 vs 240 volts.
 
Good point.

But still not so sure about MCBs.

The way it was explained to me is that the series of values aids in coordination and discrimination between breakers.

If you take the series
16, 20, 25, 32, 40, 50, 63, 80, 100
then from each point, if you go up TWO steps, then that value is ~1.6x where you started, and your downstream breaker should now reliably trip before the upstream.
 

Reply to 16, 32 and 63 as a rating in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
441
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top