J
julianacb
Hello all, excuse my bad grammar spelling etc. today i had the people from building control around to sign of my cu change
at my house,here is my question. My mum had her oven changed a little while ago and it has a design current of around 10.5 amps, the old fuse protecting was a 40 amp wired in a 10mm t+e, i have since replaced this with a 16 amp breaker and put connecters at old cooker switch and a blank plate. I done this as section h of osg states you can do this and dont need a switch if the circuit breaker is to be used as one. The inspector told me this is not Good and my interpretation is wrong. And i need a local isolation switch. I want to know what others opinion was on this he also said the oven is not fixed equipment? If im wrong fine but how do i remedy the situation its a double box do i just put the old cooker switch back on. I did do a little search before posting but could not really find what i was looking for. Any advice greatly appreciated!
I always fit an isolator switch for any appliance in kitchens...mentioning things going faulty and catching fire tends to sway most of them to my way of thinking...
Though lost one job as the clients wife was doing the interior design on a rented property and "didn't want those ugly switches on show" and they "all have to be in the back of the cabinets hidden out of sight"...no chance...he saw the point, i think she threw a fit as I've heard nowt since sticking the quote in weeks ago....
Got a job on tomorrow...re-lay a cooker supply....as previous owners rejigged the kitchen, put in a gas cooker and their spark just extended the ring for the cooker igniter and turned the old cooker/oven supply into a socket with random spur....not what I was hoping to find...was hoping it was just the usual cooker outlet plate previously swapped for a single socket...
I really hate crawling under newish build house floors (no room to move as the builders backfill them with crap and ends up like being on an assault course)...and I have to lift laminate in a cupboard to cut a hatch (Though owner is ok with it getting wrecked if thats what it takes to get access to the floor below..says he'll get a carpet if needs be for the cupboard so one saving grace)...'kin hell....this is going to be a LONG day tomorrow....still work is work...
The switch is not required for isolation.
It depends whether you think emergency switching is required for an oven.
OK for TN, then. MCB, that is. Section 537 & Table 53.4.
Sorry, just checked my definitions. I thought of 'live' conductors as including neutral, but realise 'line' does not include neutral!
Yep.
Why do people keep quoting the OSG instead of the actual regulations?
I guess its because BS7671 is pretty scary and reads like a law book! I should have said 537.2.1.1, but seeing as though that says it doesn't need to be DP, we'll just say 'It's good practice so just do it' :D
If you're not competent to do otherwise, you'd be a fool not to follow BS7671. What i mean by ''Competent'', is being able to stand up in a court of law and successfully argue your departures are technically sound and safety has not been compromised etc...!!
Well yes obviously you would be a fool not to follow the regs and like you say if you get dragged into court your goosed. And yes it wasn't really the most helpful of things, but it is a fact.
well, if following regs. meanss drilling into a RFC in the wall, i'd be wary. LOL. :furious3:
Reply to 16amp b type breaker for oven. in the UK Electrical Forum area at ElectriciansForums.net
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
Check the clearance between the back panel and/or terminal cover that you've removed. Look for small burn marks.