Im currently on with a condition report and it's a tn-s earthing arrangement with a 6mm coming off the sheath into an earthing block then a 16mm from there to the cu, now would you put 6mm as main earthing conductor as this is worse case or 16mm as it goes into the board. Or shall I put my tin hat on
 
Well according to their (NICEIC) "definitive" interpretation....if the MET is in the CU, you wont have an Earthing conductor:rolleyes2:

Surely the "means of earthing" is generally either:
a) supply sheath,
b) neutral solid link or
c) earth rod,
therefore if the earthing conductor is "that which connects the MET to an earth electrode or other means of earthing" Definition BS7671

then the earthing conductor has to be in this instance the 6mm..ie the conductor from MET to the joint on the sheath...the joint on the sheath is theirs (DNO) and they can keep it.
 
Last edited by a moderator:
Well according to their (NICEIC) "definitive" interpretation....if the MET is in the CU, you wont have an Earthing conductor:rolleyes2:

Surely the "means of earthing" is generally either:
a) supply sheath,
b) neutral solid link or
c) earth rod,
therefore if the earthing conductor is "that which connects the MET to an earth electrode or other means of earthing" Definition BS7671

then the earthing conductor has to be in this instance the 6mm..ie the conductor from MET to the joint on the sheath...the joint on the sheath is theirs (DNO) and they can keep it.

Yes this is correct as there is a met between the service head and the cu.
 
page 37 of the current bs7671 is clear as crystal if you ask me............

the conductor to the MET from whatever supply type is present is the "main" earthing conductor

the 16mm from MET to CU is actually a circuit protective conductor.

why guess when you can simply look up the facts...........


;-)
 
Last edited by a moderator:
So, he's doing an EICR, so theses are not irrelevant. TIf the Ze is within tolerance and the 16mm is from the CU. I wouldn't code it as its OK. IMH
no.

its like saying `well theres a bit of 16mm there.....but the bit where it drops to 6mm is irrelevent`..

worst case : 6mm...i would give this one a 2

sometimes i have come across where there has been 2X 10mm G/Y used as the main earthing...
i would put that down as 10mm/10mm...perfectly acceptable as long as run together and prefably taped/tiewrapped together along their run= no code..
 
So, he's doing an EICR, so theses are not irrelevant. TIf the Ze is within tolerance and the 16mm is from the CU. I wouldn't code it as its OK. IMH
no.

its like saying `well theres a bit of 16mm there.....but the bit where it drops to 6mm is irrelevent`..

worst case : 6mm...i would give this one a 2

sometimes i have come across where there has been 2X 10mm G/Y used as the main earthing...
i would put that down as 10mm/10mm...perfectly acceptable as long as run together and prefably taped/tiewrapped together along their run= no code..

Why would you give it a code 2, if calculated using the adiabatic equation and all is sufficient then it wouldn't warrant a code 2
 

Reply to 16mm or 6mm in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
918
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
A bit like saying plumbers makes good electricians. 🥴
Replies
10
Views
2K
  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top