Hi all
Im currently on with a condition report and it's a tn-s earthing arrangement with a 6mm coming off the sheath into an earthing block then a 16mm from there to the cu, now would you put 6mm as main earthing conductor as this is worse case or 16mm as it goes into the board. Or shall I put my tin hat on
Well according to their (NICEIC) "definitive" interpretation....if the MET is in the CU, you wont have an Earthing conductor:rolleyes2:
Surely the "means of earthing" is generally either:
a) supply sheath,
b) neutral solid link or
c) earth rod,
therefore if the earthing conductor is "that which connects the MET to an earth electrode or other means of earthing" Definition BS7671
then the earthing conductor has to be in this instance the 6mm..ie the conductor from MET to the joint on the sheath...the joint on the sheath is theirs (DNO) and they can keep it.
a) supply sheath,
c) earth rod,
Yes this is correct as there is a met between the service head and the cu.
page 37 of the current bs7671 is clear as crystal if you ask me............
the conductor to the MET from whatever supply type is present is the "main" earthing conductor
the 16mm from MET to CU is actually a circuit protective conductor.
why guess when you can simply look up the facts...........
So, he's doing an EICR, so theses are not irrelevant. TIf the Ze is within tolerance and the 16mm is from the CU. I wouldn't code it as its OK. IMH
no.
its like saying `well theres a bit of 16mm there.....but the bit where it drops to 6mm is irrelevent`..
worst case : 6mm...i would give this one a 2
sometimes i have come across where there has been 2X 10mm G/Y used as the main earthing...
i would put that down as 10mm/10mm...perfectly acceptable as long as run together and prefably taped/tiewrapped together along their run= no code..
no.
Why would you give it a code 2, if calculated using the adiabatic equation and all is sufficient then it wouldn't warrant a code 2
Reply to 16mm or 6mm in the UK Electrical Forum area at ElectriciansForums.net
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...