Mike Watters

periodic report says it's inadequate. was installed 10 years ago. 60 amp rewireable fuse protects the cable. the main supplies a small bed sit with 1 x lighting circuit, 1 x 32 amp radial socket circuit and 1 x cooker circuit that has a 3kw cooker. a new wylex consumer united was fitted 2 years ago. why would it be ok 2 years ago and not now.
 
Sounds fine to me. So they think its undersized? When you say sub-main is it coming from a main.board somewhere else?
Use diversity or clamp it to prove 16mm is certainly enough.

Sent from my GT-I9100 using Tapatalk
 
Not got the book to hand but from memory 16mm is good for something like 99A, so backed by a 60A CPD I can't see an issue at all.
 
from the OSG 16mm is good for 85A if clipped direct but goes down to 42.5A ref103 so I think it depends on the installation method.

I think we need more info, for example Ipf, to work out if the 6mm2 cpc is good enough.
 
The bedsit might need main protective bonding if it's seperate from the house, in which case the 6mm cpc isn't adequate.
Does the report say anything about this?

Does the report say anything about how the 16mm is installed (or can you tell us)? Mainly we need to know if it runs through any insulation or is otherwise enclosed.

If it's surface clipped or buried direct in plaster then 85A x 0.72 3036 factor = 61A, so OK.
 
115.

Thats the highest I can find for 16mm2 multicore, but thats assuming its entire length is soaked in liquid helium.

Does that mean the electricity comes out squeaky?
 

Reply to 16mm t+e sub main in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
798
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
828

Similar threads

Electric hob/oven range was installed years ago, runs on 2 x B32 MCBs to 'House' (sub)consumer panel, runs to oven on 2 x T&E. Kitchen is being...
Replies
0
Views
288
  • Question
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top