periodic report says it's inadequate. was installed 10 years ago. 60 amp rewireable fuse protects the cable. the main supplies a small bed sit with 1 x lighting circuit, 1 x 32 amp radial socket circuit and 1 x cooker circuit that has a 3kw cooker. a new wylex consumer united was fitted 2 years ago. why would it be ok 2 years ago and not now.
 
I put a 16mm T&E into a bungalow last week to facilitate a board relocation - original 16mm tails now go to a DP iso, then run to the new board via 16mm TE clipped to the loft joists. I just ran a 10mm earth alongside it from a new MET, so effectively giving it a 16mm earth as well. Cut-out is only a 60A (1 bed bungalow) so I have no problem with it all being 16mm not 25mm.
 
If its a Periodic or EICR it should explain what is inadequate and a suitable code attached to that observation.

What has been documented re the above?

What is the earthing arrangement for the premises?
 
If its a Periodic or EICR it should explain what is inadequate and a suitable code attached to that observation.

What has been documented re the above?

What is the earthing arrangement for the premises?
and while its all about "its this....its that"....the voice of sense comes forth......is it a "2"...or what?.....
 
i would not consider disconnection times not being met as a code 1 ( immediate danger ). question that comes to mind is what disconnection time was he looking for?
 
Shouldn't there be a Zs/Ipf on the PIR/EICR? Wouldn't that be enough to determine the disconnect time?
I might be getting a bit ahead of myself as I have only just started my 2395 and I am not clear whether the PIR was for the whole installation or just the sub board but I'd have though there should be enough info recorded to work out what the problem is.
 
As a C1 has been issued what has been done to take that immediate danger away and make the premises SAFE!.

A bit more info is required as this type of vauge report putting fear into people not good practice.

I don't like to guess but I would say the issue here is the 6mm earth on a TNC-S system which should be a minimum of 10mm as that is the minimum csa for the bonding conductors.

If you have the ZE the adiabatic can be worked out but due to the PME system in place table 54.8 is the reference.


On the EICR item no's 3.4 and 3.6 should have a code attached if that is the case.
 
just tried that doncaster calc. i put in 60A , 20m run, 5% VD. it came back with 6mm!!!
 

Reply to the thread, titled "16mm t+e sub main" which is posted in Australia on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top