Customer has a 25mm sub main fed into DP isolator (as pictured) then 16mm T&E out of the top to feed 2nd consumer unit about 20m away. 2nd consumer unit has 8 circuits. (1 32A Ring, 2 socket radials, 1 lights, Shower (pump fed no heater), Immersion heater, 2 Ovens). Diversity & cable rating aside surely the supply to the 2nd CU should be 16mm CPC as per OSG 4.4 not 6mm?
- Is the 6mm earth conductor supply to the 2nd CU classed as "the" earthing conductor? If so surely OSG 4.4 applies (16/16)
- or is it considered as the main protective bonding conductor in which case 6mm is still inadequate for 16mm live conductor supply isn't it? (16/10)
If the earthing conductor is inadequate do I run a 10mm earth cable alongside the run? Or rip it all out and use 20m of "proper 16mm L,N,E tails"
Thanks in advance