I am going to be changing the consumer unit in a house. The owner arranged to have an isolator switch fitted by N power (free of charge). Ive been to look at it and the guy has fitted it with 16mm tails. The customer was told that this was because the tails to the ccu are 16mm. But it has a 100amp fuse. I will be fitting a new 9.5kw shower and the cooker is electric as well as the usual ring main and lights ect. It is a 3 bed house. I was going to change the tails to the ccu to 25mm.

Am I correct in thinking that he should have fitted 25mm to the isolator switch? All the tables ive looked at say I am.
 
If you look at the fuses tripping times then I think you will find they will blow at 1.5x in an hour so even a 60A would take 90 for an hour, I wouldn't honestly worry to much. If you were in western powers area, they only give out 80A's apart from special requests, other DNO's do either 60A or 100A.
 
Nope, no way other then a physical check I'm afraid, so is a bona fide limitation!
Bear in mind if you are working in a flat and come accross a bright red fuse and carrier, this is a solid link! The fuse will be down at the incoming position to the building!
 
I tend to install 25mm tails on board changes these days as a matter of course tbh....always the possibility someone will request an upgrade to 100A in the future so at least it's sat ready waiting for it.
 

Reply to 16mm tails with 100amp fuse? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
774

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
697
  • Question
Yeh that’s my thinking. I have to supply the box so can order a bigger 3 phase option to give myself a bit more room
Replies
3
Views
838

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top