16th ed unsheathed cables | on ElectriciansForums

Discuss 16th ed unsheathed cables in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

There won't be one if you mean Permits the situation.
Do you mean the normal round Ashley type brown box where the sheath has been cut beyond the cutout in the box.?
 
History .Doing condition report on block of 90 flats put all downlights in corridors down as c2 100mm of unsheathed cable into clip type connectors and someone has just used connector strip in places no jbox ,noted relevant regs from 17th ed .what client is trying to do is hold main contractor who gave 10yr warranty on building to task .just wanted to get in front as I am expecting reply from them to be it was installed to 16th ed.
 
No regulation would allow that! Past or present!
C2 for all.
Don't know the exact numbers off hand but all live connections should be adequately enclosed and no basic insulation should be visible outside the enclosure
 
Try 526-03-03.
Cores of sheathed cables from which the sheath has been removed and non-sheathed cables at the termination of conduit, ducting or trunking shall be enclosed as required by Regulation 526-03-02.

And 521-07-03.
Non-sheathed cables for fixed wiring shall be enclosed in conduit, ducting or trunking.

BS 7671 : 1992
 
The OP has said, that the client wants to take advantage of the builder’s 10 year warranty.
Obviously, if the work did not comply at the time of construction, the client can make a claim.
 
I agree with previous comments, why the 16th edition?
Previous work carried-out which was compliant under old regulations is deemed satisfactory by current regulations, however any work that you perform now can be subject to the current regulations despite warranties.
Regardless, I'd advise my clients to change any old wiring systems to meet the current standards and explain why the standards where changed... safer for them and better business.
 
I agree with previous comments, why the 16th edition?
Previous work carried-out which was compliant under old regulations is deemed satisfactory by current regulations, however any work that you perform now can be subject to the current regulations despite warranties.
Regardless, I'd advise my clients to change any old wiring systems to meet the current standards and explain why the standards where changed... safer for them and better business.
I think you are missing the point.
The wiring is not satisfactory, and the OP wishes to know if it complied with the Regulations in force at the time of it’s design/construction.
If it did comply, the OP’s client may not be able to ask the builder to rectify under the terms of the warranty.
If it did not comply then the client will be able to ask the builder to rectify.
What you personally would do is neither here nor there.
All the OP needs to know, is whether the work complied.
 
Previous work carried-out which was compliant under old regulations is deemed satisfactory by current regulations
Not necessarily. It may or may not be satisfactory, but the simple fact that it no longer complies is not what makes it unsatisfactory.

Would you consider fused neutrals to be satisfactory if you came across them?
 

Reply to 16th ed unsheathed cables in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
268
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
755

Similar threads

I can imagine it just disappearing (loudly) under short circuit conditions, then the resulting blast/plasma etc. casing the busbars to flash over...
Replies
13
Views
695
See there is the problem. I can put back to way it was. Is it safe, in my opinion NO!! It's wasn't safe before the incident. No Fused Spur...
Replies
9
Views
514

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top