Nuisance tripping from a large transformer installation can be prvented by

A- the use of an rcd
B- the use of a c type mcb
C- the use of a b type mcb
D- the use of a d type mcb

i know the answers is D but can some please point out where in the regs to find the answer
 
2 honest mate i havent got a clue i was revising for my 17th ed exam and got some pass papers which i came across this question i got the answers but doest point out where in the regs the answer is. All i know is Type B - trips between 3 and 5 time full load current
Type C - trips between 5 and 10 times full load current
Type D - trips between 10 and 20 times full load current
 
im not 100% sure the answewr is d iv just got the questions and answers thats why i wanted 2 check it in the regs just 2b sure im hoping some one on here will be able to help
 
i suppose it depends on the current rating of the tranny wrt that of the MCB, either a c type or a d type could be rhe answer.
 
The installation, is fed from a transformer, so that would be the secondary side wouldn't it?
If overload protection can be ommitted, fault protection would still be required.
I can't actually think of any Regulation that deals with using type B, C or D MCBs on a transformer.
Could it be that the answer is to not use an MCB at all, and just use an RCD?
 
Last edited by a moderator:

Reply to 17th ed question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
920
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
If they are standard RCBOs the MCB aspect could be b,c, or d , but the RCD aspect is almost certainly 30mA instantaneous. If the MCB aspect...
    • Like
2
Replies
22
Views
2K
  • Question
In the current book (18th, amendment 2) it is under regs 433.2 and 434.2 In most domestic situations the usual approach is the whole circuit is...
Replies
3
Views
666

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top