Hi guys, I’ve just been to a customers house. It’s an old house which has a few radial and ring circuits for sockets. They want 4 extra sockets to be installed. The ring circuit is feeding the whole house (not kitchen) would it be ok to tap into the ring circuit feeding the house and add the 4 extra sockets.

Thanks guys
 
Hi guys, I’ve just been to a customers house. It’s an old house which has a few radial and ring circuits for sockets. They want 4 extra sockets to be installed. The ring circuit is feeding the whole house (not kitchen) would it be ok to tap into the ring circuit feeding the house and add the 4 extra sockets.

Thanks guys
Hi Jon,
I don't think there is a regulation about amounts of sockets on a ring. From memory the limiting factor is having the ring within 100m2.
Of course, you'll need to make sure it has 30mA RCD protection, no existing faults on the circuit, bonding in place etc etc. Plus give the correct paperwork (MWC).
 
Hi Jon....

Is it right you're newly qualified?

Its just the questions youve asked (this and the summer house thread) are both fairly simple things to work on.

If so, then all good. Youre just checking before working in someones house.


Adding to a ring.... youve got to keep it as a ring. You cant take an UNFUSED spur and add socket after socket.... With a FUSED spur, you can. You will hear a lot of references to "a spur from a spur" which is the exact same thing.


With a radial at say 16A, you can branch off wherever you like .... like a tree

If youve got the Big Brown Book, pagg 555 appendix 15 has arrangements for ring and radial final circuits
 
Hi Jon,
I don't think there is a regulation about amounts of sockets on a ring. From memory the limiting factor is having the ring within 100m2.
Of course, you'll need to make sure it has 30mA RCD protection, no existing faults on the circuit, bonding in place etc etc. Plus give the correct paperwork (MWC).
Thank you brother ! Appreciate the response
 

Reply to Extending ring in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
929
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Hi guys, I’ve been asked to install some electrics into a summer house in a council building. The summer house is some what 40 meters away...
Replies
0
Views
124
Outside socket… ok. But you say the fcu for boiler is beside the outside socket… is the boiler outside too? FCU’s have an IN and an OUT… the OUT...
Replies
2
Views
151

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top