Hi All,

I have just been checking out an installation in a 1970's house in prep for a CU change tomorrow, I noticed in one of the light switches the CPC has 180 volts to earth and 60 volts to live on it, obviously it is not earthed. Anyone any ideas what could cause this? Cheers
 
could well be an open circuit on the neutral back feeding down to the cutout fuse and back up the earth , that voltage is what you could get with this fault , it could well be induced voltage on a cpc that has not been connected ,what earthing arrangment is it TNCS TNS TT
 
Hi All,

I have just been checking out an installation in a 1970's house in prep for a CU change tomorrow, I noticed in one of the light switches the CPC has 180 volts to earth and 60 volts to live on it, obviously it is not earthed. Anyone any ideas what could cause this? Cheers

Do you know this for sure?
 
Just s a follow up to this. I changed the CU today and there is a fault on the downstairs lighting circuit N - E is 1.1 ohms, L - E and L - N is clear. So I've got a bit of fault finding to do tomorrow.
 

Reply to 180volts on CPC in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
411
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
701
davesparks
D
If any appliance has a filter or surge protection device, you will have a device that can pass a small current between the L and E or the N and E...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top