hi,

I have my 18th edition exam booked next week. I have just started to read up on the changes.
I am correct in stating that if the gas and water pipes have a plastic insulated section. At point of entry, then they do not require 10mm bonding??
Sorry if this is a stupid question....

Thanks
 
Then my question is - if bonding was there, but now not required by the regs and we were doing a rewire (say) would we remove it or leave it in place? I would be leaving it, but I'm not sure that's right (?).
 
Ok so Im driving myself crazy with this.

Gas Bonding Question.
The gas supply is fed up to the property (domestic PME ) underground in plastic pipe. It comes out of the ground in plastic to a meter box.

The feed into the property enters in copper.

Does the gas need bonding.

Picture to help

20191005_153015.jpg
 
No it doesn’t
What earth potential does a plastic pipe buried directly in the ground bring into the installation?
Only if plastic pipe is entering the building we only have the OPs word that it's plastic, Sorry misread the thread thought the OP said it entered in copper my bad apologies, Ian.
 

Reply to 18th edition and bonding to gas and water in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
426
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Do some of the free online tests. Get used to using the book. After doing this I passed mine easy enough.
Replies
8
Views
2K
  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
2
Replies
23
Views
2K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top