Stroma Certification Scheme 18th Edition email from Stroma
Non approved equipment would be a consumer unit made from old packing crates.
Non approved equipment would pertain to the current reg 133.1.1. which asks all equipment to be of a BS or BSEN standard.
We will now be asked to make record where we choose to include non standardised kit.
I would say that in domestic installations the rules will apply the same as now,plasterboard ceilings have a fire rating to a certain period of time so your plastic cable clips will still be used.
Plastic saddles for conduit however could be rendered unusable for all exposed wiring containment everywhere at high levels maybe
Chaps you should start reading the draft, and making comments on the draft.
For example re plastic clips, in the draft it says (521.10.210) 'Note 2 this regulation precludes the use of non metallic clips or cable ties as the sole mean of support where cables are clipped direct to exposed surfaces or suspended under cable tray, and the and the sole means of support of the cables therein.'
The addition of an earth rod 'may be' used....
Get reading and get commenting, save just sounding off here. You never know, if they get enough comments, they might realise how ridiculous some of their suggestions are :)
I can't currently figure out how to view it. The BSi portal does not have BS7671 under drafts when I go there. Do you have a working link ?
Right ignore that, I'm back on it through strange means. It does not appear on the portal but I found a link in a google search.
@Midwest Reg 542.1.201 states that there shall be an earth electrode supplementing any earthing facility provided by the distributor. Not may be.
So are they basically saying that the onus on providing a good earth connection moves from the DNO to the owner of the installation?
No. The DNO are not currently required to provide an earth connection as far as I am aware, just to maintain one they have provided.
This supplementary earth electrode is just that, supplementary, and additional to any other provided earth arrangement. Consider it akin to bonding.
This has been talked about for years at the IEE/IET and Paul Cook of the IEE produced an interesting paper on it over ten years ago with many people suggesting not long after that the 18th Edition should clarify/include this. Whether it will be clarified is debatable. I can see the benefit for lost neutral problems with TN-C-S systems as it would reduce the touch voltage should this occur.
Not sure which bit you can't locate, I used this link from IET; 18th Edition of BS 7671: send us your feedback - IET Electrical - http://electrical.------.org/wiring-matters/64/dpc/index.cfm
then 'log in' below Comment on. Whatever way you do use, when in the BSI web site search for - BS 7671 - (need the space between BS (&) 7671).
Stand corrected Andy. Edit, just reading 421.1.7 about AFDD's, is where I got me wires crossed, with 'may be' written there :oops:
In any case it needs further clarification, as alluded to by the many comments. I get side ways looks from my customers, when I suggest their bonding needs upgrading, when replacing a luminaire for them. They are going to think I'm a right rogue, when I spend half a day putting in some new earth rods :)
Octopus,
Strima,