Doing an EICR, one circuit described as Central Heating with 1 mm T&E cable connected but on a 16A MCB. When I look closer it appears an Immersion heater has been tagged onto the circuit!
I've not been able to ascertain the cable route and its installation method. This is a single storey extension, no loft space.
If I use Ref C then 1mm is OK (just). There is no signs of overheating at either end of the cable, insulation measurements are good. The immersion is probably seldom used (if at all) because of a boiler in use.
I guess I can't give it an Observation unless I chose another installation method.
Any comments/advice?