Doing an EICR, one circuit described as Central Heating with 1 mm T&E cable connected but on a 16A MCB. When I look closer it appears an Immersion heater has been tagged onto the circuit!

I've not been able to ascertain the cable route and its installation method. This is a single storey extension, no loft space.

If I use Ref C then 1mm is OK (just). There is no signs of overheating at either end of the cable, insulation measurements are good. The immersion is probably seldom used (if at all) because of a boiler in use.

I guess I can't give it an Observation unless I chose another installation method.

Any comments/advice?
 
Top of my head that cable is rated at about 8amps, I would not be happy if an IH, is running off that. No way is that cable suited,dangerous IMO, would give that C2.
 
If it's only feeding a central heating system then if it's connected through a switch fused spur the cable on the load side will be fused down to 3amps hopefully.
It will never pull 16amps so overload protection can be omitted plus the 3amp fuse will provide protection to the outgoing cable to the boiler.
If it's powering an immersion heater than yeah , wouldn't be happy with 16amp mcb feeding 1mm.
Cable is rated to 16amps clipped direct tho.
 
Think the norm is installing 2.5mm from db on 16amp mcb through a double pole switch and 1.5mm heat resistant flex out into immersion element
 

Reply to 1mm T&E on a 16A MCB - doesn't look or feel right! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
444
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Thanks for your time and opinion.
Replies
11
Views
1K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top