very strange issue i have here...basically my consumer unit has 2 RCD's

RCD1 : downstairs lights
Outside lights
smoke alarm(currently off)
shower(currently off)

RCD2:upstairs lights
All house sockets + boiler(boiler currenly switched off)
Cooker (currently off)

my BIG problem and i cant figure it out is when i plug my 500W drill into the house socket (on RCD 2) it trips all RCD1 off but leaves RCD2 on with no problems. also alternativly if i switch the living room lights(downstairs lighting) on and off quick they trip RCD1.

i have wired the outside lights onto RCD 2 and when i do as soon as the outside lights come on it trips RCD1.

few other things to bear in mind are - i am renovating the house so no cooker/washer/dryer /fridge/shower in use, as above says 'curretly off' means at the MCB switch is in the 'off' position.

this has only happened this week when i have started to use my drill and it has been weeks since i have messed with any electrics BUT i have been using the drill regularly in all sockets.


please help!
 
hi all

very strange issue i have here...basically my consumer unit has 2 RCD's

RCD1 : downstairs lights
Outside lights
smoke alarm(currently off)
shower(currently off)

RCD2:upstairs lights
All house sockets + boiler(boiler currenly switched off)
Cooker (currently off)

my BIG problem and i cant figure it out is when i plug my 500W drill into the house socket (on RCD 2) it trips all RCD1 off but leaves RCD2 on with no problems. also alternativly if i switch the living room lights(downstairs lighting) on and off quick they trip RCD1.

i have wired the outside lights onto RCD 2 and when i do as soon as the outside lights come on it trips RCD1.

few other things to bear in mind are - i am renovating the house so no cooker/washer/dryer /fridge/shower in use, as above says 'curretly off' means at the MCB switch is in the 'off' position.

this has only happened this week when i have started to use my drill and it has been weeks since i have messed with any electrics BUT i have been using the drill regularly in all sockets.


please help!

Sounds to me like you have borrowed neutrals between some of your circuits. More than likely your lighting circuits.
 
Last edited:
do you mean connected neutrals from diferent circuits?
i can check this.
how else do you mean "borrowedcircuits" ?[/QUO


I would check your neutrals on your hall stair lights.

In a lot of cases the 2 way circuit from bottom of stairs to top of stairs has both lights on downstairs circuit but the neutral to the top light is taken from the upstairs lighting circuit.

Worth checking.
 
Last edited:
spot on Sintra!
A borrowed neutral on the landing light as a classic one. Another one to look out for is wall lights switched from a wall switch but neutral taken from local socket.

check between the neutral bars on the CU they should be clear (Mohms)
 
'check between the neutral bars on the CU they should be clear (Mohms)' not sure what you mean by this legge?? can you expand more?


What legge means is that between the 2 neutral bars in your consumer unit with the main switch turned off you should have no connectivity. This can be checked by carrying out an insulation resistance test between the 2 neutral bars. If you have a connection between the 2 then proceed to dicsonnect neutrals in turn and retest untill you can find the culprit.
 
Each rcd has a neutral bar so with a 2 rcd board, there will be 2 neutral bars so all the circuits supplied via rcd1 will have the neutrals terminated to neutral bar 1 and all circuits supplied via rcd 2 will have the neutrals terminated to neutral bar 2.
Thus there should be no connection between neutral bars 1 and 2. Insulation readings should therefore be in the range of megaohms.
If you have any borrowed neutrals ie crossed circuits for example the landing light, then as soon as that light is turned on, the energy travelling via a live on one rcd will return via the neutral to the other rcd therefore tripping the rcd/s!
 
i will check this tomorrow and get back to you all - thanks so far!

i have 1 more question...

i have 1 spur from the MCB (2.5m) which connects to 2 sperate outside lights 1 300w and 1 500w which are on 1.5m cable each, is this acceptable and will it cause me any problems???
 
Hia there. Unsure of what you`re numbers mean - is that 2.5m? & 1.5m?

Not much to go on my friend. Better chance of help if you give more info - cable sizes & MCB rating...

Also, are you sure you`re confident, & competent to be even opening that CU, let alone doing IR testing?

No offence intended i assure you, but safety before bravery & all that ;)
 
Then if you`ve used 1.5 mm

At its simplest, I = P / V so 500w / 230 = 2.2 amps only & 1.3 amps for the 300W lamp

Clearly a fraction of the current carrying capacity of any 1.5 mm (unless you`ve routed it somewhere naughty)


As for the IR testing, have you got suitable equipment to carry this out? Not something most folk would have TBH
 

Reply to 1rcs trips when the other has use in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
904

Similar threads

Thank you, what would be the advice for me to do in this scenario? I've also seen circuits tripped in past from other things such as 1500VA step...
Replies
6
Views
514
  • Question
A kettle boiling fish - thats your fault right there... or is it a red herring? :)
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top