Hello, stating I am not an electrician,

I have purchased a fairly expensive set of used powered studio monitors and I’m concerned about one of them. I was switching the power switch at the back and I’ve switched it off quite poorly where it went back on itself and as it was half way between on and off the whole house tripped, set off the alarms etc. I assumed maybe it was some kind of arc from poorly switching off the power switch.

I then remembered the upstairs tripped the day I received them, and I think I plugged them in around the same time.

Now the other socket in my office is for some reason wired to downstairs, a week after the other incidents I switched off everything at the wall, all on an extension including this speaker, and that seemed to trip the downstairs sockets.

Happened again when I switched the power on at the wall a couple days later.

The device works fine when on, seems to be in a state of powering on or powering off.

I got out the Megger BM80 I’ve got and tested the insulation and it’s at 370MegaOhms both poles to ground.

Can anyone explain what could be happening and what I should be doing. Are there any other tests I can do. Thank you for any advice.
 
When you say tripped what type of device was it,mcb,rcbo,Arc Fault Detection Device or (RCD) Residual Current Device a picture of your consumer unit indicating which device tripped would be handy
 
Hello, stating I am not an electrician,

I have purchased a fairly expensive set of used powered studio monitors and I’m concerned about one of them. I was switching the power switch at the back and I’ve switched it off quite poorly where it went back on itself and as it was half way between on and off the whole house tripped, set off the alarms etc. I assumed maybe it was some kind of arc from poorly switching off the power switch.

I then remembered the upstairs tripped the day I received them, and I think I plugged them in around the same time.

Now the other socket in my office is for some reason wired to downstairs, a week after the other incidents I switched off everything at the wall, all on an extension including this speaker, and that seemed to trip the downstairs sockets.

Happened again when I switched the power on at the wall a couple days later.

The device works fine when on, seems to be in a state of powering on or powering off.

I got out the Megger BM80 I’ve got and tested the insulation and it’s at 370MegaOhms both poles to ground.

Can anyone explain what could be happening and what I should be doing. Are there any other tests I can do. Thank you for any advice.
Is it just the one monitor that does it ?
What is the make model ?
 
I wouldn't be at all surprised if it turns out that there is nothing wrong with your monitor, other than the dodgy power switch, but you do turn out to have some poor neutral to earth resistance somewhere else on the circuit monitored by the RCD in question.
 
When you say tripped what type of device was it,mcb,rcbo,Arc Fault Detection Device or (RCD) Residual Current Device a picture of your consumer unit indicating which device tripped would be handy
It has tripped the sockets that are marked in red, hope this helps and thank you.
 

Attachments

  • 3892546792354697386.jpg
    3892546792354697386.jpg
    469.9 KB · Views: 63
I wouldn't be at all surprised if it turns out that there is nothing wrong with your monitor, other than the dodgy power switch, but you do turn out to have some poor neutral to earth resistance somewhere else on the circuit monitored by the RCD in question.
Thank you, what would be the advice for me to do in this scenario? I've also seen circuits tripped in past from other things such as 1500VA step down converter has done it a couple times in the past also.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Powered speaker tripped circuits four times over a couple weeks, insulation tester result seems ok, need advice.
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
reprobate,
Last reply from
reprobate,
Replies
6
Views
708

Advert

TrueNAS JBOD Storage Server

Back
Top