Come on then, read the Table, and tell us your interpretation of it.

my interpretation is that as the fan is supplied from the lighting circuit, the cable spec. is that for.............





wait for it....................








............................................................................a lighting circuit.
 
those enviro fans are well good if you installed the fan the wrong way round there would be no need for the hair dryer , back to the bathroom issue , installation methods are required to select your cable size , insulation clipped direct etc personally I would only use 1.5mm , fused spur fan isolator , junction box on down lighters etc and bonding is required if even if you do have RCD protection unless install is plastic a 1 meter length of pipe in some circumstance could be an extraneous part so the pipe work should be checked supply supplementary bonding can be omitted if all circuits are RCD protected and bondings in place etc
 
Hi alani, the average bathroom fan (15W) consumes about 0.06A.
There is no way I would feel you must use 1.5mm.


Yes, I know that, but it is there in the Regs.
I asked the query on the IET site, and the answers there are indeterminate.
Smokes could be included in Note 1, but there is no definition of a power or lighting circuit in BS7671.
How about a single socket outlet, protected by a 6A CB supplying a TV only, less than a metre from the CU?
That would run fine on a 1mm T+E cable, but it wouldnt comply with Table 52.3, yet in all other respects would comply.

Yes, I know in the real world such situations dont often arise, but the original poster should think about this before installing a low wattage fan on a 1mm conductor.
 
Yes, I know that, but it is there in the Regs.
I asked the query on the IET site, and the answers there are indeterminate.
Smokes could be included in Note 1, but there is no definition of a power or lighting circuit in BS7671.
How about a single socket outlet, protected by a 6A CB supplying a TV only, less than a metre from the CU?
That would run fine on a 1mm T+E cable, but it wouldnt comply with Table 52.3, yet in all other respects would comply.


Yes, I know in the real world such situations dont often arise, but the original poster should think about this before installing a low wattage fan on a 1mm conductor.

How would installing a socket circuit that can take a 13A fuse in a plug top, protected by a 6A MCB comply with regs ?
 
That would run fine on a 1mm T+E cable, but it wouldnt comply with Table 52.3, yet in all other respects would comply.

So the cable complies in all other respects except for an arbitrary table, relating to undefined power circuits. So when is a power circuit not a power circuit then??

So what you're saying is, a 1.5mm cable needs to be installed from the CU to the bathroom to cater for a 15/20W extract fan, because the existing lighting circuit is 1mm?? Jesus, are you completely off your rocker or what??
 
It's all down to design considerations.
If we had every appliance working on a RFC, it would (probably) overload that circuit.
The Designer will take that into account, and make the assumption that all appliances will most likely not be all on at the same time, so gives it a 32A CB, which is enough for maybe half of the appliances to run together.
The same is true of a socket outlet behind a TV, it is marked as 'For use of wall TV only'.
If situated at the top of a wall, behind a TV, it is very unlikely to be used for general use, and if marked correctly, it will comply.
To be sure that it doesnt get used for other things, a 5A socket outlet and plug could be used, or even a FCU, but most people are sensible, so would not use it for anything else.
 
So the cable complies in all other respects except for an arbitrary table, relating to undefined power circuits. So when is a power circuit not a power circuit then??

So what you're saying is, a 1.5mm cable needs to be installed from the CU to the bathroom to cater for a 15/20W extract fan, because the existing lighting circuit is 1mm?? Jesus, are you completely off your rocker or what??

It isnt what I am saying, it is in the Regs.
It isnt an arbitary table is it? It is there on page 130, with Reg 524.1 pointing to that table.

The argument is, what is a power circuit?
Is it a fan, or, can a fan be spurred off a lighting circuit in 1mm, and still comply?
There are no definitions, the closest I can think of are the difference in voltage drop between lighting and 'other uses'.

Why have a rant, without explaining what you think?
 
It isnt what I am saying, it is in the Regs.
It isnt an arbitary table is it? It is there on page 130, with Reg 524.1 pointing to that table.

The argument is, what is a power circuit?
Is it a fan, or, can a fan be spurred off a lighting circuit in 1mm, and still comply?
There are no definitions, the closest I can think of are the difference in voltage drop between lighting and 'other uses'.

Why have a rant, without explaining what you think?


That's exactly what i said, you're taking notice of a table that has no definition as to what constitutes a ''power circuit''!! If a circuit electrically/mechanically complies with all the relevant criteria, then a non descriptive table can be kicked into touch as far as i'm concerned!! As usual in these situations, applying a little commonsense will show you the way!!
 

Reply to 1st install job advice please in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
791
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

Hi all, first post, please be gentle ;) Iv been involved in a bathroom refurb, nothing major, moving a light fitting and switch. My problem came...
Replies
0
Views
305
Which begs the question, where does the second brown wire come from?
Replies
5
Views
431

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top