Hi, I need to install 2 separate underfloor heat mats both rated at 17A on individual 20A breakers. The heatmat controls are rated at 16A so I think it would have to go through a contactor right? I can install an enclosure in a cupboard for the contactors but would I have to use 2 x 1 pole contactors like this, or is a 2 pole contactor like this ok with 2 separate circuits running through it.

And just out of curiosity because I havent used contactors before, would it be possible to have the power to pull the relay in switched from a seperate circuit? So a supply from a control circuit, then 2 loads on there own circuits through 1 double pole contactor.

Thanks
 
i'd first speak to manufacturers ans see if that 16A rating has a bit of latitude. if using a contactor is necessary, then a 2 pole contactor is acceptable. ( label the contactor enclosure saying "2 circuits inside" or words to that effect). use whatever you like to energise the coil as long as it's installed safely.
 
Last edited:
Most contactors have two ratings inductive and resistive. So which rating do you use bearing in mind the load? You tell me and I’ll say if you’re right or wrong, then you’ll get help.
Do a bit of the work to get the answers, not unreasonable is it?
 

Reply to 2 17A Heat Mats Through Contactor in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
401
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
988
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I've seen a few posts here which tend to suggest that wiring in a motorhome (or caravan) wouldn't be subject to normal inspection rules, but even...
Replies
0
Views
353
  • Question
It's the policy on this forum not to give step by step advice. If you have an understanding of wiring requirements you will not have any...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top