Carrying out an EICR today.

Found a radial 6mm supply, 32a, to the cooker, with a 2.5 spur off to a double socket.

Debating whether to mark down as an observations. In my mind its the same as a spur of a 32a ring main??

Thoughts please
 
agree. highly unlikely that the 6mm will be overloaded. ifit's ref.C, then it's good for 47A and it's protected by a 32A MCB. the socket is unlikely to pull over 20A, so the 2,5mm also is safe.
 
Socket rated to 13amps, cooker diversity applied so unless the circuit can be overloaded and the spur is adequately protected for fault protection it's ok
 
Sorry the Zn neutral loop impedance as to ensure the cable can withstand a short circuit fault as being supplied with a 6mm could have quite a low impedance resulting in a higher fault level.
 

Reply to 2.5 spured of a cooker supply in the Electrical Appliances Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
270
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
764

Similar threads

I would put this down to 433.3.1(ii) - no overload protection needed because the load at the single socket can't overload the cable, being fused...
Replies
14
Views
2K
  • Question
Cheers guys, enjoyed reading all the responses. I'm an apprentice and it was a conversation that came up at work between two electricians...
2 3
Replies
43
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top