I'm curious too as to what happened to the ring final circuit? Hopefully it wasn't needed for anything!
On the RFC, you are allowed a spur at the origin, and thus keep the ring.
 
You said the customer "only wanted a twin socket changed" yet you ripped out a RFC from the CU? I think that's what he is trying to say.

Apologies I didn't explain that very well, the builders on site ripped all the existing conduit out and with it the existing ring final, leaving it broken on the floor and live, so I dissed it all and put it in the skip, customer just needed one 2g putting back.

Thanks for the replies, I think despite the rating of the socket you should allow for 26A maximum, as you could in theory plug 2 x 3kw loads into it. The 2.5 cable would have been sufficient I feel and is protected from overload by the plug top fuses.

No I didn't look into getting a £5 MCB - my regular wholesaler does not stock proteus 3871 MCBs i dunno whats up with them??
 

Reply to 2.5mm on a 32a radial or not? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
620
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
954

Similar threads

I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...
Replies
4
Views
477
  • Question
Tech has totally complicated 'control' Customer wants something controlling. First job is to figure out the best method
    • Funny
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top