I'm curious too as to what happened to the ring final circuit? Hopefully it wasn't needed for anything!
On the RFC, you are allowed a spur at the origin, and thus keep the ring.
 
You said the customer "only wanted a twin socket changed" yet you ripped out a RFC from the CU? I think that's what he is trying to say.

Apologies I didn't explain that very well, the builders on site ripped all the existing conduit out and with it the existing ring final, leaving it broken on the floor and live, so I dissed it all and put it in the skip, customer just needed one 2g putting back.

Thanks for the replies, I think despite the rating of the socket you should allow for 26A maximum, as you could in theory plug 2 x 3kw loads into it. The 2.5 cable would have been sufficient I feel and is protected from overload by the plug top fuses.

No I didn't look into getting a £5 MCB - my regular wholesaler does not stock proteus 3871 MCBs i dunno whats up with them??
 

Reply to the thread, titled "2.5mm on a 32a radial or not?" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

sam400

Arms
-
Joined
Location
sussex
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
2.5mm on a 32a radial or not?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
17

Thread Tags

Advert

Thread statistics

Created
sam400,
Last reply from
sam400,
Replies
17
Views
8,270

Advert

Back
Top